#93789 - 06/17/05 10:06 PM Are concentric or eccentric knockouts evaluated for bonding?
Joe Tedesco Offline
Member
Registered: 10/07/00
Posts: 2749
Loc: Boston, Massachusetts USA
Just to be sure, you should read the following information very carefully, when evaluating concentric and eccentric knockouts:
http://www.ul.com/regulators/knockouts.cfm
_________________________
Joe Tedesco, NEC Consultant
Top
2017 / 2014 NEC & Related Books and Study Guides
#93790 - 06/18/05 01:16 AM Re: Are concentric or eccentric knockouts evaluated for bonding?
William Runkle Offline
Member
Registered: 02/11/03
Posts: 27
Loc: Dowagiac, Michigan U.S.A.
Intresting have you seen any boxes or cabinets marked? I will be looking for them but I still probably still bond bush so not to upset an inspector who hasn't seen the marking, plus just assurance that it is bonded and be ease of mind.
_________________________
William Runkle
Top
#93791 - 06/18/05 03:14 PM Re: Are concentric or eccentric knockouts evaluated for bonding?
Joe Tedesco Offline
Member
Registered: 10/07/00
Posts: 2749
Loc: Boston, Massachusetts USA
Yes,

The following table summarizes the box and enclosure categories where such an evaluation is available and how to identify compliant products that can be installed according to the exception to Section 250.97.

Category Code
Product Category
Concentric and eccentric knockouts evaluated for bonding?

BGUZ
Boxes, Junction and Pull
Only when product is marked*

CYIV
Cabinets and Cutout Boxes
Only when product is marked*

QCIT
Metallic Outlet Boxes
All products comply


* Products Listed for these applications are provided with a marking, such as "Concentric (or eccentric) knockouts suitable for bonding conduits for non-service conductors."
_________________________
Joe Tedesco, NEC Consultant
Top
#93792 - 06/23/05 01:38 PM Re: Are concentric or eccentric knockouts evaluated for bonding?
DougW Offline
Member
Registered: 06/08/03
Posts: 1143
Loc: North Chicago, IL
+1 for the additional bonding.

The $8 in parts is worth more than 20 minutes proving your point to an inspector.
Top
#93793 - 06/23/05 02:40 PM Re: Are concentric or eccentric knockouts evaluated for bonding?
tkb Offline
Member
Registered: 12/04/04
Posts: 94
Loc: Massachusetts
Just knock out the KO all the way and use reducing washers. They are UL listed for grounding. Save the cost of the bond bushings.
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (annemarie1), 67 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals