The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 6 Guests and 1 Spider online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#93789 - 06/17/05 10:06 PM Are concentric or eccentric knockouts evaluated for bonding?
Joe Tedesco Offline
Member

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
Just to be sure, you should read the following information very carefully, when evaluating concentric and eccentric knockouts:
http://www.ul.com/regulators/knockouts.cfm
_________________________
Joe Tedesco, NEC Consultant

Top
2014 / 2011 NEC & Related Books and Study Guides
#93790 - 06/18/05 01:16 AM Re: Are concentric or eccentric knockouts evaluated for bonding?
William Runkle Offline
Member

Registered: 02/11/03
Posts: 27
Loc: Dowagiac, Michigan U.S.A.
Intresting have you seen any boxes or cabinets marked? I will be looking for them but I still probably still bond bush so not to upset an inspector who hasn't seen the marking, plus just assurance that it is bonded and be ease of mind.
_________________________
William Runkle

Top
#93791 - 06/18/05 03:14 PM Re: Are concentric or eccentric knockouts evaluated for bonding?
Joe Tedesco Offline
Member

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
Yes,

The following table summarizes the box and enclosure categories where such an evaluation is available and how to identify compliant products that can be installed according to the exception to Section 250.97.

Category Code
Product Category
Concentric and eccentric knockouts evaluated for bonding?

BGUZ
Boxes, Junction and Pull
Only when product is marked*

CYIV
Cabinets and Cutout Boxes
Only when product is marked*

QCIT
Metallic Outlet Boxes
All products comply


* Products Listed for these applications are provided with a marking, such as "Concentric (or eccentric) knockouts suitable for bonding conduits for non-service conductors."
_________________________
Joe Tedesco, NEC Consultant

Top
#93792 - 06/23/05 01:38 PM Re: Are concentric or eccentric knockouts evaluated for bonding?
DougW Offline
Member

Registered: 06/08/03
Posts: 1083
Loc: North Chicago, IL
+1 for the additional bonding.

The $8 in parts is worth more than 20 minutes proving your point to an inspector.

Top
#93793 - 06/23/05 02:40 PM Re: Are concentric or eccentric knockouts evaluated for bonding?
tkb Offline
Member

Registered: 12/04/04
Posts: 94
Loc: Massachusetts
Just knock out the KO all the way and use reducing washers. They are UL listed for grounding. Save the cost of the bond bushings.