#93789 - 06/18/05 01:06 AM Are concentric or eccentric knockouts evaluated for bonding?  
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
Just to be sure, you should read the following information very carefully, when evaluating concentric and eccentric knockouts:
http://www.ul.com/regulators/knockouts.cfm


Joe Tedesco, NEC Consultant

2017 / 2014 NEC & Related Books and Study Guides

#93790 - 06/18/05 04:16 AM Re: Are concentric or eccentric knockouts evaluated for bonding?  
William Runkle  Offline
Member
Joined: Feb 2003
Posts: 27
Dowagiac, Michigan U.S.A.
Intresting have you seen any boxes or cabinets marked? I will be looking for them but I still probably still bond bush so not to upset an inspector who hasn't seen the marking, plus just assurance that it is bonded and be ease of mind.


William Runkle

#93791 - 06/18/05 06:14 PM Re: Are concentric or eccentric knockouts evaluated for bonding?  
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
Yes,

The following table summarizes the box and enclosure categories where such an evaluation is available and how to identify compliant products that can be installed according to the exception to Section 250.97.

Category Code
Product Category
Concentric and eccentric knockouts evaluated for bonding?

BGUZ
Boxes, Junction and Pull
Only when product is marked*

CYIV
Cabinets and Cutout Boxes
Only when product is marked*

QCIT
Metallic Outlet Boxes
All products comply


* Products Listed for these applications are provided with a marking, such as "Concentric (or eccentric) knockouts suitable for bonding conduits for non-service conductors."


Joe Tedesco, NEC Consultant

#93792 - 06/23/05 04:38 PM Re: Are concentric or eccentric knockouts evaluated for bonding?  
DougW  Offline
Member
Joined: Jun 2003
Posts: 1,143
North Chicago, IL
+1 for the additional bonding.

The $8 in parts is worth more than 20 minutes proving your point to an inspector.


#93793 - 06/23/05 05:40 PM Re: Are concentric or eccentric knockouts evaluated for bonding?  
tkb  Offline
Member
Joined: Dec 2004
Posts: 94
Massachusetts
Just knock out the KO all the way and use reducing washers. They are UL listed for grounding. Save the cost of the bond bushings.



Member Spotlight
Lostazhell
Lostazhell
Bakersfield, CA (Originally Orange Co.)
Posts: 1,428
Joined: February 2004
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.011s Queries: 14 (0.002s) Memory: 0.7662 MB (Peak: 0.9022 MB) Zlib enabled. Server Time: 2017-03-26 15:00:58 UTC