The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
1 registered (sparkyinak), 201 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#93774 - 06/14/05 06:07 PM main breaker for subpanel
Jim M Offline
Member

Registered: 08/10/01
Posts: 453
Loc: Chestertown, MD, USA
I just got a red tag for not having a main in a subpanel in a residential detached garage. Panel is a C-H 4/8 MLO with 2 circuits installed. AHJ is using 225-31 as the reason.

Is anyone elses area requiring this. I guess I was thinking 6 or less breakers did not need a main.

Top
2014 / 2011 NEC & Related Books and Study Guides
#93775 - 06/14/05 06:14 PM Re: main breaker for subpanel
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
In my opinion you are correct.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#93776 - 06/14/05 06:15 PM Re: main breaker for subpanel
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
225.33(A) General. The disconnecting means for each supply permitted by 225.30 shall consist of not more than six switches or six circuit breakers mounted in a single enclosure, in a group of separate enclosures, or in or on a switchboard. There shall be no more than six disconnects per supply grouped in any one location.
_________________________
Greg Fretwell

Top
#93777 - 06/14/05 09:29 PM Re: main breaker for subpanel
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
For a separate building, such as a detached garage, you are required to have a disconnecting means on the building. In this area, I typically have a 'safety switch' mounted on the outside, feeding the panel directly behind it (on the inside). A 'main breaker' in the panel is another way to do it- but is usually more expensive- and our AHJ likes the disconnect on the outside anyway.

There is one exception- no such disconnect is necessary if you're running only one circuit- and "circuit" is vague enough to include a single multi-wire branch circuit (or what we normally think of as two circuits). Assuming that you are using both full-size breaker spaces for a pair of full size breakers, you might be able to argue that you have but a single multi-wire circuit, with the breakers simpling being an additional, not required, disconnecting means.

Top
#93778 - 06/15/05 11:35 AM Re: main breaker for subpanel
JBD Offline
Member

Registered: 07/12/01
Posts: 599
Loc: WI, USA
IMO (and that of the Handbook) 225 section II effectively says to treat each separate building like it has it's own service entrance. Except when only one circuit (specifically allows multi-wire) is in the separate building.

225.30 only one source can feed the separate building (230.2, 230.40)
225.31 all ungrounded conductors must be disconnected (230.70)
225.32 disconnect where power enters building (230.71(A))
225.33 number of mains (230.71)
225.34 group the mains (230.72)
225.35 accessible to occupants (230.70(A)(1), 230.72(C))
225.36 suitable for service entrance(230.70(C))

Top
#93779 - 06/15/05 12:39 PM Re: main breaker for subpanel
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
Don't ignore 225.36 exception
Exception: For garages and outbuildings on residential property, a snap switch or a set of 3-way or 4-way snap switches shall be permitted as the disconnecting means.
_________________________
Greg Fretwell

Top
#93780 - 06/15/05 04:02 PM Re: main breaker for subpanel
luckyshadow Offline
Member

Registered: 01/04/05
Posts: 305
Loc: Maryland USA
Where I live if the sub panel is in a ATTACHED garage no main needed - in a DETACHED garage a main is required by ahj

Top
#93781 - 06/15/05 05:23 PM Re: main breaker for subpanel
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
Thank you, JBD, for taking the time to break down all the code citations I was alluding to!