#93756 - 06/11/05 11:55 PM Motor Starters
Wireless Offline
Member
Registered: 06/09/05
Posts: 73
Loc: Los Angeles CA USA
Im new to posting but have been reading all the forums for a while great stuff!

On to my question we are setting up some panning machines with 1hp motors they are on a 20amp branch circuit with a fused disconnect do I need a overload protection starter as well or just a magnetic contactor?
Your replies are appreciated
Top
2017 / 2014 NEC & Related Books and Study Guides
#93757 - 06/12/05 04:54 AM Re: Motor Starters
Tom Offline
Member
Registered: 01/01/01
Posts: 1044
Loc: Shinnston, WV USA
If these motors are single phase, they may have built in overload protection, read the data plate.

If these are 3 phase motors, then it is unlikely that they will have overload protection & you will have to supply it.

Tom
_________________________
Few things are harder to put up with than the annoyance of a good example.
Top
#93758 - 06/12/05 05:04 AM Re: Motor Starters
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
The NEC requires all motors to have some sort of overload protection.

That may well be already provided in the motor or it may not be, as Tom stated.

Take a look at 430.32(B) or 430.32(D) depending on if the motors are automatically started or not.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#93759 - 06/12/05 09:27 AM Re: Motor Starters
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
IBM used a buttload of 3p motors in their equipment and they all had O/L protection in the motor but you do have to read it on the nameplate to believe it.
_________________________
Greg Fretwell
Top
#93760 - 06/12/05 07:59 PM Re: Motor Starters
macmikeman Offline
Member
Registered: 07/16/02
Posts: 717
Loc: Honolulu, Hawaii
Aren't those little clicks- on overload protectors that come on three phase AC compressors used for other purposes besides AC/ Reefer motors?
Top
#93761 - 06/12/05 09:56 PM Re: Motor Starters
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
Don't forget about the possibility of an impedance protected motor or the fact that sometimes the Short Circuit and Ground Fault device can also serve as the overload device per 430.55
_________________________
George Little
Top
#93762 - 09/01/05 08:14 PM Re: Motor Starters
jack1984 Offline
Junior Member
Registered: 08/28/05
Posts: 1
Loc: los angeles
you should know that most starters and motors have a variety of ways to be wired what exact type is your starter and motor
Top

Member Spotlight
Member Since: 08/22/05
Posts: 44
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 41 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals