Is romex (NM) allowed to be used in the walls and ceilings of a horse barn in areas specified by 547.1 where it will be concealed by a finish surface such as wood on the walls and plastered ceilings?

shortcircuit
Top
2017 / 2014 NEC & Related Books and Study Guides
#93736 - 06/08/05 04:41 PM Re: Horse Barn Wiring Methods
Gregtaylor Offline
Member
Registered: 03/02/05
Posts: 212
Loc: Boise, Idaho, USA
The way I read it, I think you're OK.
Top
#93737 - 06/09/05 11:02 AM Re: Horse Barn Wiring Methods
shortcircuit Offline
Member
Registered: 06/27/04
Posts: 608
Loc: massachusetts
Can anyone explain what the last sentance of 334.10(3) means or maybe have a link to such list as described?

"Cables shall be concealed within walls, floors, or ceilings that provide a thermal barrier of material that has at least a 15-minute finish rating as identified in listings of fire-rated assemblies."

My concern is if romex (NM) is concealed behind finish walls of wood on the interior of a horse barn, is the wood wall finish acceptable as a 15-minute fire-rated assembly?

shortcircuit
Top
#93738 - 06/09/05 12:04 PM Re: Horse Barn Wiring Methods
earlydean Offline
Member
Registered: 12/22/03
Posts: 751
Loc: Griswold, CT, USA
As I recall, 1/2 inch wallboard has a 15 minute rating.
Let me check the UL book for others.
_________________________
Earl
Top
#93739 - 06/09/05 12:17 PM Re: Horse Barn Wiring Methods
earlydean Offline
Member
Registered: 12/22/03
Posts: 751
Loc: Griswold, CT, USA
Nope, no wood. All the listed assemblies are gypsum wallboard, plaster, cement block, masonry or 24 gauge metal panels.
_________________________
Earl
Top
#93740 - 06/09/05 12:19 PM Re: Horse Barn Wiring Methods
earlydean Offline
Member
Registered: 12/22/03
Posts: 751
Loc: Griswold, CT, USA
Oh yeah, and concrete.
_________________________
Earl
Top
#93741 - 06/09/05 12:53 PM Re: Horse Barn Wiring Methods
earlydean Offline
Member
Registered: 12/22/03
Posts: 751
Loc: Griswold, CT, USA
Now you got me going.

My rule of thumb is just not sufficient. the finish ratings go all over the chart, depending on the manufacturer and the product. Examples: American Gypsum Co. 5/8 inch Gypsum board Types AGX-1,2&3 have 23 minute finish ratings. AGX-5 has a 26 minute finish rating. US Gypsum Co. 1/2 inch Gypsum Wallboard (GWB) Types AR, FRX-G, SCX, SHX or WRX all have a 29 minute finish rating.
There are hundreds more. But, the lowest rating I could find for 1/2 inch GWB was 20 minutes. The rating for some 3/8 inch GWB was 8 minutes, so watch out!
The assembly also required paper tape over the joints, and usually a minimum of 2 coats of joint finishing compound.

Sounds like, to make your installation code compliant, you need to add 1/2 GWB over the walls of the barn where you have run the romex.
_________________________
Earl
Top
#93742 - 06/09/05 01:12 PM Re: Horse Barn Wiring Methods
earlydean Offline
Member
Registered: 12/22/03
Posts: 751
Loc: Griswold, CT, USA
You can research them yourself at: http://www.ul.com/fire/building.html
Click on the picture of the front cover of the building materials directory.
_________________________
Earl
Top
#93743 - 06/09/05 01:15 PM Re: Horse Barn Wiring Methods
earlydean Offline
Member
Registered: 12/22/03
Posts: 751
Loc: Griswold, CT, USA
http://database.ul.com/cgi-bin/XYV/templ...73741824&ve rsion=versionless&parent_id=1073984818&sequence=1
_________________________
Earl
Top
#93744 - 06/09/05 01:58 PM Re: Horse Barn Wiring Methods
shortcircuit Offline
Member
Registered: 06/27/04
Posts: 608
Loc: massachusetts
Thanx earlydean, but I couldn't navigate through to where I could find specific listings on sheetrock and wood?

shortcircuit
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (ghost307), 67 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals