The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
International Wire Colour Codes
by Tjia1981
Today at 09:09 PM
Son of Sparky
by HotLine1
Yesterday at 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
230 or 345 kV transmission lines?
by annemarie1
10/12/16 01:23 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
HotLine1 6
renosteinke 6
ghost307 5
Potseal 4
Who's Online
0 registered (), 139 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#93694 - 06/07/05 02:22 PM Hot tub disconnect.
Edward Offline

Registered: 12/14/02
Posts: 309
Loc: California
Does a hot tub need a disconnect at the site? Or a GFCI breaker will suffice out of site.
I know in a commercial non residential setting there is a emergency disconnect required. How about a residential setting?

Thanks in many ways.

2014 / 2011 NEC & Related Books and Study Guides
#93695 - 06/07/05 04:20 PM Re: Hot tub disconnect.
shortcircuit Offline

Registered: 06/27/04
Posts: 608
Loc: massachusetts
680.12 requires the disconnect to be readily accessible and within sight of the equipment that it serves...