The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Today at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
Yesterday at 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Texas_Ranger 8
Trumpy 8
sparkyinak 7
Who's Online
0 registered (), 218 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#93635 - 05/26/05 11:41 AM fire & security on separate circuits
jsherrard Offline
Member

Registered: 07/10/04
Posts: 18
On a recent project (10,000 sq ft place of assembly) the fire protection inspector required two changes to the electrical work during final inspection. First, he directed that the fire alarm panel and the building security panel could not be fed by the same circuit as the plans had indicated. He made a reference to NFPA 72. (This was transmitted to me by the owner's agent. The electrical work had already passed final inspection.) Does anyone know the specific rule he might have been referencing? Also, he required that emergency lights be installed in the 2 public restrooms. No specific reason was given to support this. Again, is anyone aware of a national code that would require this?

Top
2014 / 2011 NEC & Related Books and Study Guides
#93636 - 06/02/05 10:01 AM Re: fire & security on separate circuits
Ryan_J Offline
Moderator

Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
This thread has been moved from the Building Codes Forum to here. If anyone has any input on the subject, please post it here.
_________________________
Ryan Jackson,
Salt Lake City

Top
#93637 - 06/03/05 06:50 AM Re: fire & security on separate circuits
Last Leg Offline
Member

Registered: 05/04/05
Posts: 41
Loc: Houston, Texas
NFPA (National Fire Protection Association)encompasses NFPA 72, which covers 'Fire Alarm', and NFPA 70 (NEC), along with a host of other 'codes'. It stands to reason that a circuit that provides power to a LIFE SAFETY system should be isolated. Also, emergency egress lighting is required for certain Building Occupancy types for the public. This is probably in NFPA 72, or maybe the UBC. Don't know the specifics.. ask you Fire Alarm installer, he should probably know precisely.

Top
#93638 - 12/03/05 09:12 AM Re: fire & security on separate circuits
Paul O'Connell Offline
Member

Registered: 07/02/05
Posts: 57
Loc: Allen Park, Mi. USA
JS:

NFPA 72 requires the firealarm panel be on a seperate circuit. It also requires that that location of that circuit be posted on the front of the FACP. On the emergency light you would find that in NFPA 101. Though I think you may have difficulty finding that exact violation listed there.

Top
#93639 - 12/03/05 09:17 AM Re: fire & security on separate circuits
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Paul the bathroom violation is in the NEC although it may also be in 101. Check out the second paragraph of 700.16

 Quote:
700.16 Emergency Illumination.
Emergency illumination shall include all required means of egress lighting, illuminated exit signs, and all other lights specified as necessary to provide required illumination.

Emergency lighting systems shall be designed and installed so that the failure of any individual lighting element, such as the burning out of a light bulb, cannot leave in total darkness any space that requires emergency illumination.

Where high-intensity discharge lighting such as high- and low-pressure sodium, mercury vapor, and metal halide is used as the sole source of normal illumination, the emergency lighting system shall be required to operate until normal illumination has been restored.

Exception: Alternative means that ensure emergency lighting illumination level is maintained shall be permitted.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#93640 - 12/03/05 02:41 PM Re: fire & security on separate circuits
jsherrard Offline
Member

Registered: 07/10/04
Posts: 18
Iwire, ... I'm not sure I understand your comment. The reference in the NEC you cited (as I understand it) means that the failure of a single lamp on the emergency light itself cannot leave the area without emergency illumination, therefore emergency lights come with two heads to satisfy that requirement. How does this address whether or not emergency lighting is required in a restroom?

Top
#93641 - 12/03/05 06:35 PM Re: fire & security on separate circuits
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Sorry I misread your post, I skimmed through and thought he was requiring two heads in one bathroom.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#93642 - 12/04/05 01:15 PM Re: fire & security on separate circuits
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
"two heads in one bathroom" I get it - Bob said a funny
_________________________
George Little

Top
#93643 - 12/04/05 03:54 PM Re: fire & security on separate circuits
Ron Offline
Member

Registered: 03/13/02
Posts: 577
Loc: White Plains, NY
NFPA 72-2002 4.4.1.4.1 requires a dedicated branch circuit for the primary power to the FACP.

Generally, the building code requires emergency lighting if there are two doors or more to the room.
_________________________
Ron

Top
#93644 - 12/04/05 04:18 PM Re: fire & security on separate circuits
earlydean Offline
Member

Registered: 12/22/03
Posts: 749
Loc: Griswold, CT, USA
Normally, bathrooms, closets, one man offices and the like do not require an emergency light.
The means of egress is required to be illuminated to one footcandle. The means of egress consists of exit access, exits and exit discharge. Exit access is anywhere one can stand and move about, so technically, that includes the bathrooms. Not too many inspectors will require them in there, however.
Check the plans. If the plans were approved by the building department at plan review without emergency lights in the bathrooms, then you have a case to appeal this decision. The fire marshal is required to check the plans as well.