#93505 - 05/29/05 12:52 PM GFI for spas
GTE Offline
Member
Registered: 03/26/03
Posts: 48
Loc: Bridgehampton, N.Y. USA
Does the NEC require GFCI protection for a hard wired spa with a light?
Top
2017 / 2014 NEC & Related Books and Study Guides
#93506 - 05/30/05 08:59 AM Re: GFI for spas
dana1028 Offline
Member
Registered: 01/09/02
Posts: 163
Loc: San Carlos, CA
"Does the NEC require GFCI protection for a hardwired spa with a light?"

Is it fair to interpret this to mean the light is inside the spa...underwater luminare?

If so:

680 Part IV - Spas & Hot Tubs
680.42 - Outdoor Locations
"A spa hot tub installed outdoors shall comply with the provisions of Parts I & II..."

680.23(A)(3) (Part II) - "A GFCI shall be installed in the branch circuit supplying luminares..."

680.43 - Indoor Locations
680.43(B)(2) - Underwater Applications - "Underwater luminares shall comply with the provisions of 680.23 or 680.33."

Sounds like you need GFCI protection.
Top
#93507 - 05/30/05 10:01 AM Re: GFI for spas
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
It is easier than that.


680.44 Protection.
Except as otherwise provided in this section, the outlet(s) that supplies a self-contained spa or hot tub, a packaged spa or hot tub equipment assembly, or a field-assembled spa or hot tub shall be protected by a ground-fault circuit interrupter.

(A) Listed Units. If so marked, a listed self-contained unit or listed packaged equipment assembly that includes integral ground-fault circuit-interrupter protection for all electrical parts within the unit or assembly (pumps, air blowers, heaters, lights, controls, sanitizer generators, wiring, and so forth) shall be permitted without additional GFCI protection.
(B) Other Units. A field assembled spa or hot tub rated 3 phase or rated over 250 volts or with a heater load of more than 50 amperes shall not require the supply to be protected by a ground-fault circuit interrupter.
(C) Combination Pool and Spa or Hot Tub. A combination pool/hot tub or spa assembly commonly bonded need not be protected by a ground-fault circuit interrupter.
_________________________
Greg Fretwell
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Forum Styles
by Admin
Today at 02:22 PM
License exam
by TRUE POWER
Yesterday at 09:16 PM
Looking for older post
by sparkyinak
Yesterday at 12:27 AM
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM

Who's Online
0 registered (), 99 Guests and 19 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 08/17/06
Posts: 358

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals