The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 137 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#93494 - 05/28/05 05:36 PM Metalic Raceway Grounding
shortcircuit Offline
Member

Registered: 06/27/04
Posts: 608
Loc: massachusetts
I have been installing PVC underground to supply outdoor branch circuits. PVC makes for a speedy installation.

I have had some of this PVC damaged from impact, including SCH 80 where it emerges from ground.

I want to use a piece of ridged conduit only where it emerges from ground and change right back to PVC.

Does the code require this short section used for physical protection to be bonded to the grounding conductor of the branch circuit?

shortcircuit

Top
2014 / 2011 NEC & Related Books and Study Guides
#93495 - 05/28/05 06:28 PM Re: Metalic Raceway Grounding
Joe Tedesco Offline
Member

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
Yes.
_________________________
Joe Tedesco, NEC Consultant

Top
#93496 - 05/28/05 07:05 PM Re: Metalic Raceway Grounding
Gregtaylor Offline
Member

Registered: 03/02/05
Posts: 212
Loc: Boise, Idaho, USA
I can never find this code article when I need it, including now, but Joe is right. If you use a short piece of rigid in a run of PVC (some guys like to use rigid 90's including me) the only way it doesn't need bonding is to be 24" or more underground.

Top
#93497 - 05/28/05 08:34 PM Re: Metalic Raceway Grounding
Joe Tedesco Offline
Member

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
See 250.80, Exception, and 250.86, Exception No. 3
_________________________
Joe Tedesco, NEC Consultant

Top
#93498 - 05/28/05 08:55 PM Re: Metalic Raceway Grounding
Gregtaylor Offline
Member

Registered: 03/02/05
Posts: 212
Loc: Boise, Idaho, USA
Oops. 18".

Top
#93499 - 05/28/05 09:32 PM Re: Metalic Raceway Grounding
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
Can you drop a short sleeve of RMC over the PVC where it is subject to "severe" damage.
_________________________
Greg Fretwell

Top
#93500 - 05/28/05 10:34 PM Re: Metalic Raceway Grounding
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Greg- I like that idea of slipping a piece of RMC or IMC over the PVC. And you wouldn't even have to bond it
_________________________
George Little

Top
#93501 - 05/29/05 02:56 AM Re: Metalic Raceway Grounding
shortcircuit Offline
Member

Registered: 06/27/04
Posts: 608
Loc: massachusetts
gfretwell...I too, like that sleeve idea and will try it!

250.86 exception #2 allows short sections of metalic raceway to be ungrounded where used to protect cable assemblies...

So, if it where UF wire emerging from ground, then no bonding...

But, if the raceway encloses individual conductors for the branch circuit, then bonding is required...

Do we agree?

shortcircuit

Top
#93502 - 05/29/05 06:48 AM Re: Metalic Raceway Grounding
harold endean Offline
Member

Registered: 02/16/02
Posts: 2248
Loc: Boonton, NJ
I asked an EC for that same idea. He had an underground 400 amp service and where the pipe came up through the floor in the basement, he sleeve the PVC riser with Ridgid and he didn't have to worry about his kids ( or anyone else) hitting the PVC riser and cracking the pipe. I think this guy went even one better and stuck some concrete inside of the RMC.

Top
#93503 - 05/29/05 10:14 AM Re: Metalic Raceway Grounding
Active 1 Offline
Member

Registered: 02/22/03
Posts: 684
Loc: Grayslake IL, USA
What is the advantage Of sleving the PVC with RMC compared to using only RMC at the stub up? I seen it specked out but just never seen any advantage.

Tom

Top