ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#93494 - 05/28/05 05:36 PM Metalic Raceway Grounding
shortcircuit Offline
Member
Registered: 06/27/04
Posts: 608
Loc: massachusetts
I have been installing PVC underground to supply outdoor branch circuits. PVC makes for a speedy installation.

I have had some of this PVC damaged from impact, including SCH 80 where it emerges from ground.

I want to use a piece of ridged conduit only where it emerges from ground and change right back to PVC.

Does the code require this short section used for physical protection to be bonded to the grounding conductor of the branch circuit?

shortcircuit
Top
2017 / 2014 NEC & Related Books and Study Guides
#93495 - 05/28/05 06:28 PM Re: Metalic Raceway Grounding
Joe Tedesco Offline
Member
Registered: 10/07/00
Posts: 2749
Loc: Boston, Massachusetts USA
Yes.
_________________________
Joe Tedesco, NEC Consultant
Top
#93496 - 05/28/05 07:05 PM Re: Metalic Raceway Grounding
Gregtaylor Offline
Member
Registered: 03/02/05
Posts: 212
Loc: Boise, Idaho, USA
I can never find this code article when I need it, including now, but Joe is right. If you use a short piece of rigid in a run of PVC (some guys like to use rigid 90's including me) the only way it doesn't need bonding is to be 24" or more underground.
Top
#93497 - 05/28/05 08:34 PM Re: Metalic Raceway Grounding
Joe Tedesco Offline
Member
Registered: 10/07/00
Posts: 2749
Loc: Boston, Massachusetts USA
See 250.80, Exception, and 250.86, Exception No. 3
_________________________
Joe Tedesco, NEC Consultant
Top
#93498 - 05/28/05 08:55 PM Re: Metalic Raceway Grounding
Gregtaylor Offline
Member
Registered: 03/02/05
Posts: 212
Loc: Boise, Idaho, USA
Oops. 18".
Top
#93499 - 05/28/05 09:32 PM Re: Metalic Raceway Grounding
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
Can you drop a short sleeve of RMC over the PVC where it is subject to "severe" damage.
_________________________
Greg Fretwell
Top
#93500 - 05/28/05 10:34 PM Re: Metalic Raceway Grounding
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
Greg- I like that idea of slipping a piece of RMC or IMC over the PVC. And you wouldn't even have to bond it
_________________________
George Little
Top
#93501 - 05/29/05 02:56 AM Re: Metalic Raceway Grounding
shortcircuit Offline
Member
Registered: 06/27/04
Posts: 608
Loc: massachusetts
gfretwell...I too, like that sleeve idea and will try it!

250.86 exception #2 allows short sections of metalic raceway to be ungrounded where used to protect cable assemblies...

So, if it where UF wire emerging from ground, then no bonding...

But, if the raceway encloses individual conductors for the branch circuit, then bonding is required...

Do we agree?

shortcircuit
Top
#93502 - 05/29/05 06:48 AM Re: Metalic Raceway Grounding
harold endean Offline
Member
Registered: 02/16/02
Posts: 2233
Loc: Boonton, NJ
I asked an EC for that same idea. He had an underground 400 amp service and where the pipe came up through the floor in the basement, he sleeve the PVC riser with Ridgid and he didn't have to worry about his kids ( or anyone else) hitting the PVC riser and cracking the pipe. I think this guy went even one better and stuck some concrete inside of the RMC.
Top
#93503 - 05/29/05 10:14 AM Re: Metalic Raceway Grounding
Active 1 Offline
Member
Registered: 02/22/03
Posts: 687
Loc: Grayslake IL, USA
What is the advantage Of sleving the PVC with RMC compared to using only RMC at the stub up? I seen it specked out but just never seen any advantage.

Tom
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 54 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals