ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

ECN Shout Chat
Top Posters(30 Days)
Admin 17
Recent Posts
Old decora style outlets
by Admin. 03/25/17 11:40 AM
ESA Arc flash course
by TheShockDoctors. 03/24/17 10:15 AM
fuse rejectors
by HotLine1. 03/24/17 07:53 AM
Another Forum Update
by Admin. 03/22/17 03:04 PM
Dining room plugs
by watersparkfalls. 03/21/17 10:31 PM
New in the Gallery:
SE cable question
Popular Topics(Views)
231,432 Are you busy
166,150 Re: Forum
160,606 Need opinion
Who's Online Now
0 registered members (), 80 guests, and 10 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#93380 - 05/20/05 01:14 PM Grounding Rod for Spa  
skingusmc  Offline
Member
Joined: May 2004
Posts: 116
Simi Valley, CA USA
Is there a requirement to have an aditional grounding rod installed (driven) near a spa (hot tub) disconnect?

This is one of those above ground, sitting on a concrete pad, plug in type of hot tubs.


Thanks
Steve

2017 / 2014 NEC & Related Books and Study Guides

#93381 - 05/20/05 04:19 PM Re: Grounding Rod for Spa  
Ryan_J  Offline
Moderator
Joined: Aug 2003
Posts: 1,374
West Jordan, Utah, USA
No.


Ryan Jackson,
Salt Lake City

#93382 - 05/21/05 08:35 AM Re: Grounding Rod for Spa  
Speedy Petey  Offline
Member
Joined: Aug 2003
Posts: 173
Upstate, NY
I don't think the term "grounding electrode" even appears in Art.680.

I can't for the life of me figure why folks continually think one is required for a spa or pool.

Just goes to show how confusing 680 can be.


Speedy Petey

"Anyone who has never made a mistake has never tried anything new." -Albert Einstein

#93383 - 05/21/05 08:58 AM Re: Grounding Rod for Spa  
Electricmanscott  Offline
Member
Joined: Jan 2002
Posts: 1,457
Holden, MA USA
I don't know if 680 is overly confusing. I think grounding and bonding in general is though. And sometimes we overthink things to the point where we start to question what is actually required or not. Whatever the case I don't know how people come up with the idea of a ground rod at a pool or spa.


#93384 - 05/23/05 12:06 AM Re: Grounding Rod for Spa  
skingusmc  Offline
Member
Joined: May 2004
Posts: 116
Simi Valley, CA USA
Thank you all for your response. I didn't "think" we would need an additional grounding rod, but wanted to ask you experts to be sure.

Thanks
Steve


Thanks
Steve

#93385 - 05/23/05 01:13 PM Re: Grounding Rod for Spa  
markp  Offline
Member
Joined: Apr 2004
Posts: 60
Kent, WA, USA
Is that spa {on} a detached structure? If so, what is powering it, a single branch circuit or a feeder? If this is a feeder to a detached structure, I can see how you could be required to establish a grounding electrode system.


Mark
Kent, WA

#93386 - 05/23/05 09:06 PM Re: Grounding Rod for Spa  
harold endean  Offline
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
I am not saying that it is required but sometimes the manufactures put it in their instructions. They will type in a sentence which might read like, "Additional ground rod might be needed. check with your local electrical code." Then some HO might install the rod thinking that they need it.


#93387 - 05/24/05 10:30 PM Re: Grounding Rod for Spa  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,799
Brick, NJ USA
Harold:
I can't resist....
AG pool, HO permit....two (2) rods, 6'6" apart, with #4 bare stranded, "butched" into the motor lug and the 'bond lugs' all around the pool (every upright), and then....back to the house, thru the basement, pipe clamps at the water main; meter jumped again, and into the panel.

Another HO "special" (as-built).....the jacuzzi wired with a 14 ga. orange extension cord; caps cut; twisted & taped splices......and a #8 solid bond to the PVC water pipes!! He had the gall to 'blame' the 'orange apron' guy for selling him the 'wrong' wire.

John


John

#93388 - 05/28/05 06:23 PM Re: Grounding Rod for Spa  
harold endean  Offline
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
John,

Yeah, I have seen that too. I was inspecting an above ground pool and the lady was showing me a trench about 100 feet long and she had about 50 of it covered up. I looked in the bottom of the trench (which was at the proper depth) but only to see that white pipe with the "Rated for 40 PSI" on it. She had used water pipe for the run. When I told her that she would have to dig it up and bury the right pipe, she was a little mad. When I opened my big mouth and said that an "Electrician" would have know the difference between water pipe and electrical conduit, then she got even madder at me. She looked at me and said, "My husband is an electrician!" I replied back, "Oops! Sorry, but it is still wrong and it has to be changed. Call it back into the office when it is done." I guess the Big Orange box gave him a good price on it.



Member Spotlight
TOOL_5150
TOOL_5150
Bay Area
Posts: 61
Joined: August 2007
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.015s Queries: 14 (0.002s) Memory: 0.7986 MB (Peak: 0.9667 MB) Zlib enabled. Server Time: 2017-03-25 17:27:49 UTC