#93376 - 05/19/05 07:22 PM Disconnect for each building
mhulbert Offline
Member
Registered: 10/19/04
Posts: 132
Loc: Anaheim, CA USA
I am ruuning power to a shower building at a camp. Exactly 8' away is another building (restrooms) that need power as well. I am mounting a 3R subpanel on the exterior of the shower building, on the wall facing the restrooms. Is it sufficient to use this subpanel as the disconnecting means for the restroom building, or should they get their own subpanel as well? There will be 3 circuits going into the restrooms. I know that I have to ground the piping + a ground rod at both of the buildings, however, it makes little sense to put up 2 subpanels 8' apart, when one will have more than enough capacity to serve both buildings.

Is 230.70 the right section to be reading for feeds to outbuildings? It says services, but I seem to remember part of the code referring me back to 230.70 when dealing with disconects on seperate structures.
Any help is apreciated!
Mike
Top
2017 / 2014 NEC & Related Books and Study Guides
#93377 - 05/20/05 02:05 AM Re: Disconnect for each building
shortcircuit Offline
Member
Registered: 06/27/04
Posts: 608
Loc: massachusetts
According to 225.30, you will need a seperate feeder with a disconnect (225.31) at each building or structure, and it must be suitable for use as service equipment (225.36)

shortcircuit
Top
#93378 - 05/20/05 07:09 AM Re: Disconnect for each building
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
"sub panel" and "disconnect" can be one and the same. Not only do some models allow you to replace the switch with breakers, the advent of hot tubs has led to the offering of many small (2 or 4 space) panels- all suitable for outside use.
Top
#93379 - 06/02/05 07:32 PM Re: Disconnect for each building
tdhorne Offline
Member
Registered: 03/22/01
Posts: 345
Loc: Maryland, USA
That second building can only have one source of supply. None of the exceptions apply to your situation. The code does not permit you to run multiple general use branch circuits from one building to another.
--
Tom Horne

225.30 Number of Supplies.
Where more than one building or other structure is on the same property and under single management, each additional building or other structure served that is on the load side of the service disconnecting means shall be supplied by one feeder or branch circuit unless permitted in 225.30(A) through (E). For the purpose of this section, a multiwire branch circuit shall be considered a single circuit.

Dam, Tom, Learn to read Shortcircuit already said that.

[This message has been edited by tdhorne (edited 06-02-2005).]
_________________________
Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 51 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 79
HotLine1 51
Ruben Rocha 29
gfretwell 25
Trumpy 20
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals