The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Members: Did you know?
by Admin
37 minutes 25 seconds ago
Safety at heights?
by HotLine1
Yesterday at 08:51 PM
International Wire Colour Codes
by Texas_Ranger
Yesterday at 03:29 PM
Looking for older post
by Texas_Ranger
Yesterday at 03:22 PM
Last time to chat here
by Trumpy
01/20/17 11:41 PM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
Admin 36
HotLine1 20
Ruben Rocha 17
gfretwell 16
Trumpy 15
Who's Online
1 registered (Admin), 81 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#93370 - 05/19/05 05:39 PM T- tap
George Little Offline
Member
Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Can you T-tap in a fire alarm system for addressable devices? Code references please.
_________________________
George Little
Top
2017 / 2014 NEC & Related Books and Study Guides
#93371 - 05/20/05 06:03 AM Re: T- tap
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 826
Loc: Michigan
All map net systems per UL listing can be T t_-Taped , Even the horns and lights if your using the approved type.
Top
#93372 - 05/20/05 10:20 AM Re: T- tap
Ron Offline
Member
Registered: 03/13/02
Posts: 577
Loc: White Plains, NY
You can t-tap a Class 'B' addressable SLC loop if the project specifications permit. No code violation.
A class 'A' loop cannot be t-taped.
See http://electrical-contractor.net/ubb/Forum2/HTML/002083.html

[This message has been edited by Ron (edited 05-20-2005).]
_________________________
Ron
Top