The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 275 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#93370 - 05/19/05 05:39 PM T- tap
George Little Offline

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Can you T-tap in a fire alarm system for addressable devices? Code references please.
George Little

2014 / 2011 NEC & Related Books and Study Guides
#93371 - 05/20/05 06:03 AM Re: T- tap
Yoopersup Offline

Registered: 03/04/03
Posts: 826
Loc: Michigan
All map net systems per UL listing can be T t_-Taped , Even the horns and lights if your using the approved type.

#93372 - 05/20/05 10:20 AM Re: T- tap
Ron Offline

Registered: 03/13/02
Posts: 577
Loc: White Plains, NY
You can t-tap a Class 'B' addressable SLC loop if the project specifications permit. No code violation.
A class 'A' loop cannot be t-taped.

[This message has been edited by Ron (edited 05-20-2005).]