The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
39 minutes 26 seconds ago
Calling all Non-US members!! (Non-US only)
by aussie240
Yesterday at 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
sparkyinak 8
Texas_Ranger 8
Trumpy 6
Who's Online
0 registered (), 234 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#93344 - 05/17/05 09:23 PM Spa User Controls, 1 pole or 2?
BigB Offline
Member

Registered: 03/31/04
Posts: 727
Loc: Tucson, AZ USA
The situation is an outdoor, in ground spa. The equipment is located remotely. There are three motors, each one 240 volts. There is a two pole switch at each motor which disconnects all the ungrounded conductors for service. In addition, the subpanel for the equipment is within sight and only four feet away. The customer wants switches located inside the wall (15 feet from the spa) as the old pneumatic system has failed somewhere underground.

Now, opinions aside, does the 2002 code require these user controls to disconnect all ungrounded conductors? What I read says "One or more means to open all ungrounded conductors". So there already exists two means to disconnect both ungrounded conductors at each motor, I can't see where the user controls would be required to do the same.

Top
2014 / 2011 NEC & Related Books and Study Guides
#93345 - 05/18/05 03:32 PM Re: Spa User Controls, 1 pole or 2?
John Crighton Offline
Member

Registered: 05/16/05
Posts: 172
Loc: Southern California
Since you've already got proper disconnecting means, the switch(es) are "motor controllers" per 430.81(A).

Per 430.84: The [motor] controller shall not be required to open all conductors to the motor.

However, the switch must also be rated for the motor load -- see 430.83(C).

Disclaimer: I'm not an electrician. I just read a lot.

Top
#93346 - 05/18/05 04:56 PM Re: Spa User Controls, 1 pole or 2?
Gregtaylor Offline
Member

Registered: 03/02/05
Posts: 212
Loc: Boise, Idaho, USA
The pertinent article is 680. If this is a single family home and you have other proper disconnecting means, the switch you are referring to isn't required at all. If you put it in however it must comply with 680.41. It is not required to open all ungrounded conductors, merely to stop the motors that provide power to the recirculating and jet system.

Top
#93347 - 05/18/05 07:59 PM Re: Spa User Controls, 1 pole or 2?
BigB Offline
Member

Registered: 03/31/04
Posts: 727
Loc: Tucson, AZ USA
Thanks guys.

Top
#93348 - 05/19/05 05:55 PM Re: Spa User Controls, 1 pole or 2?
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
I think we need to look at the code in 404.15(B) and maybe you would re-think you answer. I say that the switch needs to break all ungrounded conductors.
_________________________
George Little

Top
#93349 - 05/20/05 10:55 AM Re: Spa User Controls, 1 pole or 2?
John Crighton Offline
Member

Registered: 05/16/05
Posts: 172
Loc: Southern California
George,

Excellent point. Darn, I crawled all over 404 before answering, but I didn't expect to find the answer under a paragraph titled "Marking"! I believe I stand corrected.

So the only switch (as a motor controller) NOT required to open all conductors would be one that has no OFF label???

In that case, 430.84 would only apply to magnetic or automatic (e.g., pressure) switches, and not to manual switches, which would obviously have to be labeled with an OFF position.

But what about a 240-volt air compressor having a pressure switch that breaks only one conductor? If the On-Off "switch" is just a lever that disables the activation of the pressure switch, doesn't this violate 404.15(B)?

Anyway, back to BigB: Given that (1) both ungrounded conductors have to break, and (2) there are three motors that probably all want to run or stop simultaneously, and (3) those motors are probably upwards of 1 HP anyway, it sure looks like the snap switch wants to be the 120V pilot circuit for a group of contactors, hey?