The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
Texas_Ranger 8
Trumpy 8
sparkyinak 7
Who's Online
1 registered (LongRunner), 90 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#93236 - 05/09/05 04:53 PM Hydromasage Bathtub Bonding
shortcircuit Offline
Member

Registered: 06/27/04
Posts: 608
Loc: massachusetts
They have reworded 680.74 of the 2005 NEC covering bonding of hydromassage tubs.

I now interpet that I am only required to bond metalic piping and grounded metalic parts in "contact" with the circulating water of the hydromassage tub.

So would a metalic drain kit used with the hydromassage tub, which is not in "contact" with the circulating water and not a grounded metalic part be required to be bonded under the new wording?

shortcircuit

Top
2014 / 2011 NEC & Related Books and Study Guides
#93237 - 05/09/05 05:29 PM Re: Hydromasage Bathtub Bonding
dana1028 Offline
Member

Registered: 01/09/02
Posts: 163
Loc: San Carlos, CA
shortcircuit - this is a tough one.

Both Ryan (Utah) and myself have spoken extensively with UL about this..the principle engineer at UL for Swimming Pools, tubs, etc. was active in getting this code section revised. He also attends a monthly meeting of inspectors/contractors in San Jose.

The bottom line after much discussion with UL is pretty much this:

If you have a double insulated motor (plastic motor housing with no bonding lug) you DO NOT bond to the water piping or anything else. BTW - these motors are designed such that no part of the circulating water comes into contact with any motor component[thus the language in 2005].

If you have a regular hydromassage tub (i.e. it is not a double insulated motor) then the motor does have a bonding lug on it and it should be bonded....also most any inspector will require it to be bonded if there is a bonding lug on the motor.

Another BTW - only about 1 in 10 of these hydro tubs is double insulated (in our area).

Even though the language has changed there does not seem to be any difference in the installation than pre-2005 (pre-2005 you did not bond to double insulated motors, you did bond regular motors.....it's still the same).

If you want to speak directly with this principle engineer:

Gary.L.Higgins@us.ul.com

Top
#93238 - 05/09/05 06:33 PM Re: Hydromasage Bathtub Bonding
harold endean Offline
Member

Registered: 02/16/02
Posts: 2248
Loc: Boonton, NJ
Let's take this a couple of steps farther. What if the motor does not have a bonding lug but it is not a double insulated motor? Do you need to bond it?

How about if all the piping (Hot/cold) water pipes are plastic do you need to bond it? How about to the water spout it might be metal even though the pipes are plastic.

Top