The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
sparkyinak 9
Texas_Ranger 8
Potseal 6
Who's Online
0 registered (), 194 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#93197 - 05/06/05 07:31 AM 480/277 panel feed with straight 480
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
Can a 480/277 Sub panel be feed with straight 480 plus ground??? No neutral loads are required. All loads straight 480 v 3 phase.

Top
2014 / 2011 NEC & Related Books and Study Guides
#93198 - 05/06/05 08:59 AM Re: 480/277 panel feed with straight 480
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
Found my answer , (NO) 240.85 the breakers that fit in a 227/480 volt panel are rated 277 to ground and they must be rated 480 volt to ground incase the hookup feeding the panel is a 480 volt Delta not a Y.
Yoopersup

Top
#93199 - 05/06/05 03:10 PM Re: 480/277 panel feed with straight 480
tkb Offline
Member

Registered: 12/04/04
Posts: 94
Loc: Massachusetts
But the power will still be a Y system, just without the neutral connection.
It will still be 277 to ground unless you have a real 480 delta.
This is not uncommon in many industrial facilities.
I would just remove the neutral bar and re label the voltage on the panel.
Most likely would voilate the listing of the panel though. I would still be able to sleep at night though.

Top
#93200 - 05/08/05 03:27 PM Re: 480/277 panel feed with straight 480
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
Not if fed with a True Delta secondary not a Y which is common in many Industral applications /

Top
#93201 - 05/08/05 07:31 PM Re: 480/277 panel feed with straight 480
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
tkb,
A 3 phase wye secondary without a connection to XO is an ungrounded system and would require 480 volt breakers. It only becomes 277v to ground when you bond XO. This system behaves exactly like an ungrounded delta and there is no way to tell the difference without looking at the transformer itself.
Don
_________________________
Don(resqcapt19)

Top
#93202 - 05/09/05 08:21 AM Re: 480/277 panel feed with straight 480
pdh Offline
Member

Registered: 01/20/05
Posts: 354
Just to add to resqcapt19's post, a wye secondary could be bonded to ground at an end, such as X1, and then it would behave much like a corner grounded closed delta. That could be a suitable replacement transformer for an existing corner grounded delta system.

Now a question is, if the supply really is 480Y/277 at the source (X0 bonded), and the conductors brought to the panel are only X1,X2,X3 and G (not neutral), can you still safely and legally use 480/277 ratings? One thing you obviously cannot do is connect any 1-pole 277 volt loads. But 2-pole and 3-pole breakers (such as EDB series for Square-D NF panels) would be rated at 480/277 volts, so I would think they can be used even though the neutral is absent.

If this is an ungrounded or impedance grounded system, then it has to be treated as a pure 480 volt system since under a single-fault condition, it actually will be. And 240.85 limits 480/277 breakers to only solidy grounded systems with (not more than) 277 volts to ground. I assume Yoopersup's "straight 480 plus ground" could be a corner grounded delta where you cannot use 480/277 rated breakers (unless you know for sure otherwise, assume the worst). But can you use them if the system is definitely a 480Y/277 even if the neutral is not present?

Top
#93203 - 05/09/05 12:18 PM Re: 480/277 panel feed with straight 480
JBD Offline
Member

Registered: 07/12/01
Posts: 599
Loc: WI, USA
Voltages ratings for panelboards are line->line and line->ground. The presence, or absence, of a grounded conductor is not germane. As long as the system is a solidly grounded wye the "slash" ratings of the equipment may be used.

Top