#93168 - 05/05/05 09:16 PM Detached Building
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
If I want to run 2 circuits to a detached building in the residential setting, do I have to install a sub panel? I say you do???
_________________________
George Little
Top
2017 / 2014 NEC & Related Books and Study Guides
#93169 - 05/05/05 09:28 PM Re: Detached Building
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
You can run a single multiwire feeding 2 120v legs but not 2 separate circuits ... the way I see it.
_________________________
Greg Fretwell
Top
#93170 - 05/06/05 05:26 AM Re: Detached Building
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 822
Loc: Michigan
Wouldn't 225.36 Exception Apply.
Top
#93171 - 05/06/05 04:36 PM Re: Detached Building
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
Ernie- 225.30 limit's you to one supply with additional supplies for special conditions and residential homes can't qualify for any of these special conditions. So at best we could run a multiwire branch circuit and call it one circuit like Greg says. And I agree.
_________________________
George Little
Top
#93172 - 05/06/05 10:29 PM Re: Detached Building
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
I think the real intent is that all remote buildings get a panel, ground etc like an "HO guage service" but they make an exception for the guy who just wants a light and a receptacle in his shed. It probably makes a few less orange cords strung through the trees.
_________________________
Greg Fretwell
Top
#93173 - 05/06/05 10:32 PM Re: Detached Building
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
Now the obligatory "gee whiz" question.
If the feeder is #10/3wg with a 30a sub panel, what size wire do you run to the ground rod?
_________________________
Greg Fretwell
Top
#93174 - 05/07/05 08:06 AM Re: Detached Building
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
And the "obligatory" answer is minimum #8 cu.
I liked that word"obligatory" so I thought I'd use it in the answer, must be the inspector in me. Could use #6 AL if you could figure out some way to keep it 18" above the earth.
_________________________
George Little
Top
#93175 - 05/07/05 10:03 AM Re: Detached Building
Electric Ian Offline
Member
Registered: 02/10/04
Posts: 133
Loc: MA, USA
Do you think Table 250.66 note 2 might allow you to use a #10 here ? Using the argument that the feeders to the subpanel are not Service Entrance Conductors and thus the "equivalent" size service entrance conductors to feed the load would be (is, in fact) #10.
Top
#93176 - 05/07/05 10:23 AM Re: Detached Building
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
How about if I connect the two structures with a fence?
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#93177 - 05/07/05 10:31 AM Re: Detached Building
Electric Ian Offline
Member
Registered: 02/10/04
Posts: 133
Loc: MA, USA
I don't think the fence can make a difference. If joining 2 structures with a fence creates a single structure than I live in my neighbors house. Or does he live in mine
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 61 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals