The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Today at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
Yesterday at 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Texas_Ranger 8
Trumpy 8
sparkyinak 7
Who's Online
0 registered (), 218 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#93164 - 05/05/05 06:13 PM Garage service feeds house
Active 1 Offline
Member

Registered: 02/22/03
Posts: 684
Loc: Grayslake IL, USA
I looked at a house with a strange set up with the service. The service drop is overhead about 20' to the garage. On the back of the garage is the mast and meter. Inside is a 100a fused disco. Then the load side gos underground in 2" about 30' to the house load center.

I can't find anything in the NEC about this. I keep thinking I read it's not permited some where but maybe I'm thinking of a local thing some place.

They are doing an addition so a larger service will be needed. If keeping with a simular set up what would the proper way to bond and ground? I would say a G-rod at the house and garage plus cold water at the house. Bond only the disco & meter at the garage and pull a EG to the house panel. The house panel would have a insulated nutral bar.

I would proibly just use a meter socket with a built in ocp.

Right now the garage circuit is just double taped of the load side of the disco and gos to a single 20a breaker. Could I just put it on a breaker in the house and run the garage circuit with the house feeders?

Tom
Tom

Top
2014 / 2011 NEC & Related Books and Study Guides
#93165 - 05/05/05 09:34 PM Re: Garage service feeds house
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
What's the question? The house has a sub panel, the garage is the main building with the service disconnect. Whether you need a 3 wire or 4 wire feeder (reground the neutral etc) depends on if there are other metalic paths. You do need a ground electrode system at both buildings.
_________________________
Greg Fretwell

Top
#93166 - 05/06/05 05:23 AM Re: Garage service feeds house
Active 1 Offline
Member

Registered: 02/22/03
Posts: 684
Loc: Grayslake IL, USA
Sorry for not being to the point.

Can the house have a sub panel with the service in a detached garage?

Tom

Top
#93167 - 05/06/05 09:25 AM Re: Garage service feeds house
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
That is not unusual. It is an easy way to increase the service size for a garage shop when the house service was OK. The NEC is silent on which building the service disconnect needs to be in/on.
_________________________
Greg Fretwell