#93084 - 05/02/05 02:45 AM GFI's
JerryB52 Offline
Junior Member
Registered: 01/10/05
Posts: 2
Loc: West Palm Beach, Fl., USA
I've started with a new company and they like to use the least amount of GFI's as they can. I've mostly worked commercial but now am faced with a lot of residential jobs.

How many receptacles can safely be added to the load side of a GFI ?

Thanks
Top
2017 / 2014 NEC & Related Books and Study Guides
#93085 - 05/02/05 03:03 AM Re: GFI's
Roger Offline
Member
Registered: 05/18/02
Posts: 1716
Loc: N.C.
There is no limit as far as the NEC (with the exception of 110.3(B)) is concerened, it would be mandated by any instructions from manufacturer, which is where 110.3(B) comes in.

Roger
Top
#93086 - 05/03/05 01:28 AM Re: GFI's
JerryB52 Offline
Junior Member
Registered: 01/10/05
Posts: 2
Loc: West Palm Beach, Fl., USA
Thanks.
Most of the jobs in the past have been commercial and we put a GFI at each location that it was required.

One of the other electricians that I work with, that has done a lot of residential work told me that as a rule of thumb, no more than 4 receptacles on the load side of the GFI.
This sounds about right to me.
Top
#93087 - 05/03/05 06:35 AM Re: GFI's
Larry Fine Offline
Member
Registered: 02/18/05
Posts: 693
Loc: Richmond, VA
There is no such rule. Every GFCI receptacle I've seen has been feed-through rated for 20 amps, and is considered protected by the circuit over-current device.

There is no need to cascade GFCI's. One GFCI will provide protection for down-stream receptacles (all of them) as long as it is properly connected.
_________________________
Larry Fine
Fine Electric Co.
fineelectricco.com
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (gfretwell), 90 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals