The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 198 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#93084 - 05/02/05 02:45 AM GFI's
JerryB52 Offline
Junior Member

Registered: 01/10/05
Posts: 2
Loc: West Palm Beach, Fl., USA
I've started with a new company and they like to use the least amount of GFI's as they can. I've mostly worked commercial but now am faced with a lot of residential jobs.

How many receptacles can safely be added to the load side of a GFI ?

Thanks

Top
2014 / 2011 NEC & Related Books and Study Guides
#93085 - 05/02/05 03:03 AM Re: GFI's
Roger Offline
Member

Registered: 05/18/02
Posts: 1779
Loc: N.C.
There is no limit as far as the NEC (with the exception of 110.3(B)) is concerened, it would be mandated by any instructions from manufacturer, which is where 110.3(B) comes in.

Roger

Top
#93086 - 05/03/05 01:28 AM Re: GFI's
JerryB52 Offline
Junior Member

Registered: 01/10/05
Posts: 2
Loc: West Palm Beach, Fl., USA
Thanks.
Most of the jobs in the past have been commercial and we put a GFI at each location that it was required.

One of the other electricians that I work with, that has done a lot of residential work told me that as a rule of thumb, no more than 4 receptacles on the load side of the GFI.
This sounds about right to me.

Top
#93087 - 05/03/05 06:35 AM Re: GFI's
Larry Fine Offline
Member

Registered: 02/18/05
Posts: 684
Loc: Richmond, VA
There is no such rule. Every GFCI receptacle I've seen has been feed-through rated for 20 amps, and is considered protected by the circuit over-current device.

There is no need to cascade GFCI's. One GFCI will provide protection for down-stream receptacles (all of them) as long as it is properly connected.
_________________________
Larry Fine
Fine Electric Co.
fineelectricco.com