Should the ground rod installed for lightning protection measure less than 25 ohms to ground?

[This message has been edited by George Little (edited 04-30-2005).]
_________________________
George Little
Top
2017 / 2014 NEC & Related Books and Study Guides
#93066 - 04/30/05 07:48 PM Re: Ground rods
PCBelarge Offline
Member
Registered: 06/08/03
Posts: 681
Loc: Dobbs Ferry, NY, USA
George
That is a good question.I looked in a few of my resources and did not see any minimum value given as a point of reference.
I did see a minimum of an 8 ft ground rod that shall extend 10 feet vertically in the earth.
_________________________
Pierre Belarge
Top
#93067 - 04/30/05 09:53 PM Re: Ground rods
Larry Fine Offline
Member
Registered: 02/18/05
Posts: 693
Loc: Richmond, VA
"...an 8 ft ground rod that shall extend 10 feet vertically..."

This I gotta see!

[This message has been edited by Larry Fine (edited 05-01-2005).]
_________________________
Larry Fine
Fine Electric Co.
fineelectricco.com
Top
#93068 - 05/01/05 03:45 AM Re: Ground rods
Roxie Offline
Junior Member
Registered: 04/05/05
Posts: 6
simple, dig a hole 2 ft deep and drive the rod to the bottom, cover with dirt
Top
#93069 - 05/01/05 06:51 AM Re: Ground rods
Ron Offline
Member
Registered: 03/13/02
Posts: 582
Loc: White Plains, NY
Because that lightning protection ground rod gets bonded to the building's grounding electrode system, your results/regulation is by the NEC (more than one rod, no maximum resistance).
NFPA 780 doesn't have a maximum resistance established that I'm aware of.
_________________________
Ron
Top
#93070 - 05/01/05 06:53 AM Re: Ground rods
PCBelarge Offline
Member
Registered: 06/08/03
Posts: 681
Loc: Dobbs Ferry, NY, USA
Larry
That is a requirement from NFPA 780-Standard for the Installation of Lightning Protection Systems.
3.13.1 & 3.13.1.1
Ths standard has an illustration that shows an 8' groundrod buried 2' to make up the 10' vertical burial depth.

I have seen this done many times, as it seems the big homes and larger office buildings are all installing lightning protection these days.
_________________________
Pierre Belarge
Top
#93071 - 05/01/05 09:08 AM Re: Ground rods
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
If you do a radio tower you will see guys who are serious about ground electrodes.
I inspected a bunch of Florida DOT "radio equipment shelters" (the little shack under the tower).
They use a Ufer, coupled to ground rods (up to 40') at the corners, a ground ring and buried radials out from there. Everything is cadwelded.
_________________________
Greg Fretwell
Top
#93072 - 05/01/05 09:14 AM Re: Ground rods
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
Greg don't you live in the lightning capitol of the world?
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#93073 - 05/01/05 02:52 PM Re: Ground rods
Larry Fine Offline
Member
Registered: 02/18/05
Posts: 693
Loc: Richmond, VA
Yes, Roxie and PC, I knew that. It just struck me funny the way you (PC) worded it.

About two years ago, we did the ground work for a cellular phone tower. Rods every four feet along the ground ring, which was solid #2 tinned copper, and all spliced exothermically welded; all in a 2'+ ditch.
_________________________
Larry Fine
Fine Electric Co.
fineelectricco.com
Top
#93074 - 05/02/05 08:25 AM Re: Ground rods
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
Insight from another northern guy....what about a 10' x 3/4" rod????

BTW, anoyone ever install Lyncole Grounding devices?? Now that was a 'trip'!

John
_________________________
John
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 08/22/05
Posts: 44
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 30 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals