#93051 - 04/27/05 03:26 AM 680 GFCI Protected wiring
Steve Miller Offline
Member
Registered: 08/30/01
Posts: 325
Loc: Loudoun Cty, VA
This quote is from 680-5 in the 99 code:
"(c) Wiring. Conductors on the load side of a ground-fault circuit interrupter or of a transformer, used to comply with the provisions of section 680-20(a)(1), shall not occupy raceway, boxes, or enclosures containing other conductors unless the other conductors are protected by ground-fault circuit interrupters or are grounding conductors."
Anybody know where this is in the 02 code? or is it removed?
Top
2017 / 2014 NEC & Related Books and Study Guides
#93052 - 04/27/05 08:52 AM Re: 680 GFCI Protected wiring
gfretwell Online   content


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
680.23(F)(3) if this is the light.
_________________________
Greg Fretwell
Top
#93053 - 04/27/05 11:58 AM Re: 680 GFCI Protected wiring
Steve Miller Offline
Member
Registered: 08/30/01
Posts: 325
Loc: Loudoun Cty, VA
That's it ...thanks ... I must have looked for an hour and couldn't find it.
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (gfretwell), 95 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals