The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Members: Non-Members: Did you know?
by Admin
Today at 02:34 PM
Safety at heights?
by HotLine1
Yesterday at 08:51 PM
International Wire Colour Codes
by Texas_Ranger
Yesterday at 03:29 PM
Looking for older post
by Texas_Ranger
Yesterday at 03:22 PM
Last time to chat here
by Trumpy
01/20/17 11:41 PM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
Admin 36
HotLine1 20
Ruben Rocha 17
gfretwell 16
Trumpy 15
Who's Online
1 registered (Admin), 83 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#92995 - 04/22/05 01:54 PM Laundry circuit
George Little Offline
Member
Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Since the code talks to a 20a laundry circuit and no voltage is mentioned, am I still to figure 1500va for the laundry circuit when the appliance ask for a 15a 240v circuit? This is the rating on some of these "off shore" washers that I am seeing in the new homes lately.
_________________________
George Little
Top
2017 / 2014 NEC & Related Books and Study Guides
#92996 - 04/22/05 02:49 PM Re: Laundry circuit
Roger Offline
Member
Registered: 05/18/02
Posts: 1779
Loc: N.C.
George, 1500va would still need to be figured. I guess we could leave out the neutral consideration if we knew the unit would be 240v. In any case the NEC does note a two wire circuit.

Roger

[This message has been edited by Roger (edited 04-22-2005).]
Top
#92997 - 04/22/05 05:20 PM Re: Laundry circuit
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
Joe T has a point...it is his opinion that the NEC requires a 120v laundry circuit, even if the unit is 240v.

I agree with his reading of the code...I'm not sure I'd apply it. Heck, I recently saw some apartments that had added stack washer/dryer units to the kitchens...darned if I can sort out all the code issues that brings up!

As for the load calculations....as I see it, you'll have to do the square foot calc, and then add the known load of the appliance.
Top
#92998 - 04/22/05 05:55 PM Re: Laundry circuit
George Little Offline
Member
Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
What's Joe T? Are you talking about Joe Tedesco? and I don't see his point on this page?? I agree that it is assumed to be 120v. but even if it is 240v. the wire is the same and one could easily change the receptacle and breaker at minimal cost. But the va. would be different.
_________________________
George Little
Top
#92999 - 04/22/05 08:18 PM Re: Laundry circuit
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
I agree 120v is not specified. Perhaps if we really thought there was going to be 240v appliances you could run 12/3 and use one of those 120/240 duplexes.
The load calc is still going to be 1500va. It is an arbitrary number.
_________________________
Greg Fretwell
Top
#93000 - 04/22/05 10:25 PM Re: Laundry circuit
caselec Offline
Member
Registered: 04/14/02
Posts: 557
Loc: San Jose, CA
210.52 Lists the requirements for 125-volt 15 and 20 amp receptacles outlets in dwellings. 210.52(F) requires that a receptacle be provided for laundry. In my opinion all receptacles required in 210.52 (A) – (H) must be 125-volt.
_________________________
Curt Swartz
Top
#93001 - 04/23/05 04:49 AM Re: Laundry circuit
George Little Offline
Member
Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Good call Caselec, I agree. That one got past me. I told you guys that us inspectors learn from this forum
_________________________
George Little
Top
#93002 - 04/23/05 10:22 AM Re: Laundry circuit
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
Yes, I meant Joe Tedesco, and he has raised this point elsewhere........I was only giving credit where it was due :-)
Top
#93003 - 04/26/05 05:39 PM Re: Laundry circuit
GEC-1 Offline
Member
Registered: 06/06/01
Posts: 32
Loc: Covington, Georgia USA
I am wiring condos right now that require a 240v for the combined washer and dryer. I still provide a 120v for the washer ( even though it does not use it) to comply with the code. I asked the AHJ about this, and he said that the only way around that is if the owners were providing the washing equiptment with the condos. ( which by the way they are) But I still provide this circuit for an outlet in that space. ( a good place to hang your dust buster)
Top
#93004 - 04/26/05 09:20 PM Re: Laundry circuit
Larry Fine Offline
Member
Registered: 02/18/05
Posts: 684
Loc: Richmond, VA
I had the same situation: building owners supplying 240-v stacked units. The AHJ still wanted 120-v receptacles. Reason: appliances can be replaced, and they don't want someone needing an extension cord.

How about gas applainces that could be replaced with electric ones later? I just finished roughing a house with gas, and I suggested, and ran, a 240-v circuit just in case, to be blanked off for now.
_________________________
Larry Fine
Fine Electric Co.
fineelectricco.com
Top