#92964 - 04/21/05 05:22 AM Taps to branch circuits?
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
Would it be proper to tap a 20a circuit at each outlet with a short (6 inch) piece of #14 wire to install a duplex 15a receptacle? I seem to remember a discussion on this before but can't find the code reference. Only thing I find is 210.19(A)(4)(c) and it says "No" Comments please.
_________________________
George Little
Top
2017 / 2014 NEC & Related Books and Study Guides
#92965 - 04/21/05 05:37 AM Re: Taps to branch circuits?
shortcircuit Offline
Member
Registered: 06/27/04
Posts: 608
Loc: massachusetts
240.4(D) restricts #14 to be connected to a 15 amp overcurrent device...

Now, there are exceptions to this rule, but as you pointed out, 210.19(4) exception No. 1(c) spells out the restriction of taps connected to receptacle outlets...

shortcircuit
Top
#92966 - 04/21/05 10:09 AM Re: Taps to branch circuits?
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
There is an exception for lamp holders and luminaires but I don't think that extends to a receptacle. Receptacles are the reason for 240.4(D) in the first place IMHO. The installer has no control over what a user does so they build the 80% safety factor into the installation.
_________________________
Greg Fretwell
Top
#92967 - 04/21/05 07:52 PM Re: Taps to branch circuits?
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
Code is pretty blunt in saying that you can't do this with receptacles...you can put 15 amp receptacles on a 20 amp circuit, but you can't pigtail with #14- even though general tap rules would otherwise allow it.

I, for one, do not understand why code denies this practice. Are they trying to prevent the use of cheap 'back-stab' receptacles on 20 amp circuits? Your guess is as good as anyones'.
Top
#92968 - 06/23/05 06:50 PM Re: Taps to branch circuits?
JimMichaels Offline
Member
Registered: 05/28/04
Posts: 11
It would seem reasonable for a single 15a receptacle ... until a cube tap gets plugged in. A duplex would need dual 15a taps. Hence, NO!
Top
#92969 - 06/24/05 08:58 AM Re: Taps to branch circuits?
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
In George's question he implied that all of this tap would be inside a box so the hazard is probably not there but it is still a <technical> code violation. If this was simply to pigtail in a receptacle I doubt anyone would ever actually have any problems.
_________________________
Greg Fretwell
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 55 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals