The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
1 registered (Tjia1981), 85 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#92964 - 04/21/05 05:22 AM Taps to branch circuits?
George Little Offline

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Would it be proper to tap a 20a circuit at each outlet with a short (6 inch) piece of #14 wire to install a duplex 15a receptacle? I seem to remember a discussion on this before but can't find the code reference. Only thing I find is 210.19(A)(4)(c) and it says "No" Comments please.
George Little

2014 / 2011 NEC & Related Books and Study Guides
#92965 - 04/21/05 05:37 AM Re: Taps to branch circuits?
shortcircuit Offline

Registered: 06/27/04
Posts: 608
Loc: massachusetts
240.4(D) restricts #14 to be connected to a 15 amp overcurrent device...

Now, there are exceptions to this rule, but as you pointed out, 210.19(4) exception No. 1(c) spells out the restriction of taps connected to receptacle outlets...


#92966 - 04/21/05 10:09 AM Re: Taps to branch circuits?
gfretwell Offline


Registered: 07/20/04
Posts: 9026
Loc: Estero,Fl,usa
There is an exception for lamp holders and luminaires but I don't think that extends to a receptacle. Receptacles are the reason for 240.4(D) in the first place IMHO. The installer has no control over what a user does so they build the 80% safety factor into the installation.
Greg Fretwell

#92967 - 04/21/05 07:52 PM Re: Taps to branch circuits?
renosteinke Offline
Cat Servant

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
Code is pretty blunt in saying that you can't do this with can put 15 amp receptacles on a 20 amp circuit, but you can't pigtail with #14- even though general tap rules would otherwise allow it.

I, for one, do not understand why code denies this practice. Are they trying to prevent the use of cheap 'back-stab' receptacles on 20 amp circuits? Your guess is as good as anyones'.

#92968 - 06/23/05 06:50 PM Re: Taps to branch circuits?
JimMichaels Offline

Registered: 05/28/04
Posts: 12
It would seem reasonable for a single 15a receptacle ... until a cube tap gets plugged in. A duplex would need dual 15a taps. Hence, NO!

#92969 - 06/24/05 08:58 AM Re: Taps to branch circuits?
gfretwell Offline


Registered: 07/20/04
Posts: 9026
Loc: Estero,Fl,usa
In George's question he implied that all of this tap would be inside a box so the hazard is probably not there but it is still a code violation. If this was simply to pigtail in a receptacle I doubt anyone would ever actually have any problems.
Greg Fretwell