The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 03:17 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 8
Trumpy 6
Who's Online
0 registered (), 192 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#92947 - 04/18/05 06:22 PM expansion joints
gserve Offline
Member

Registered: 03/11/03
Posts: 92
Would a expansion joint be required under a mobile home where the feeder PVC merges from the ground to the homes feeder conduit?

Top
2014 / 2011 NEC & Related Books and Study Guides
#92948 - 04/18/05 06:46 PM Re: expansion joints
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
352.44 addresses expansion joints for RNC in accordance with expansion/contraction due to temperature change.
That being said, I've seen several instances where the Meter Sockets have been pulled off the wall from the ground settling and where remaining KO rings have been pushed through into the Meter Socket due to the ground heaving. If you suspect ground movement, an expansion joint might be a good idea.