#92947 - 04/18/05 06:22 PM expansion joints
gserve Offline
Member
Registered: 03/11/03
Posts: 92
Would a expansion joint be required under a mobile home where the feeder PVC merges from the ground to the homes feeder conduit?
Top
2017 / 2014 NEC & Related Books and Study Guides
#92948 - 04/18/05 06:46 PM Re: expansion joints
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
352.44 addresses expansion joints for RNC in accordance with expansion/contraction due to temperature change.
That being said, I've seen several instances where the Meter Sockets have been pulled off the wall from the ground settling and where remaining KO rings have been pushed through into the Meter Socket due to the ground heaving. If you suspect ground movement, an expansion joint might be a good idea.