Would a expansion joint be required under a mobile home where the feeder PVC merges from the ground to the homes feeder conduit?
Top
2017 / 2014 NEC & Related Books and Study Guides
#92948 - 04/18/05 06:46 PM Re: expansion joints
Redsy Offline
Member
Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
352.44 addresses expansion joints for RNC in accordance with expansion/contraction due to temperature change.
That being said, I've seen several instances where the Meter Sockets have been pulled off the wall from the ground settling and where remaining KO rings have been pushed through into the Meter Socket due to the ground heaving. If you suspect ground movement, an expansion joint might be a good idea.
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Looking for older post
by sparkyinak
Today at 12:27 AM
License exam
by TRUE POWER
Yesterday at 11:33 PM
Members: Non-Members: Did you know?
by Admin
Yesterday at 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM

Who's Online
0 registered (), 76 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Tom
Tom
Member Since: 01/01/01
Posts: 1069

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals