#92868 - 04/14/05 10:51 AM Recreational Vehicle Parks (551) Part VII
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 822
Loc: Michigan
What is the mosty cost effect way to wire a Park?? Since voltage Drop is so great The only way I can come up with is several Panels in Different areas with feeders back to the main building Then to the feeders to the Local breakers and outlets.551.77 prohibits Back to Back outlet locationa also. Is there a standard witdth required for theses sites>??
Top
2017 / 2014 NEC & Related Books and Study Guides
#92869 - 04/14/05 07:54 PM Re: Recreational Vehicle Parks (551) Part VII
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
The best way is to let the utility do the work at medium voltage with transformers servine a few sites apiece like they do on residential streets. Long runs with 240/120 is always going to be a copper mine.
_________________________
Greg Fretwell
Top
#92870 - 04/15/05 05:00 AM Re: Recreational Vehicle Parks (551) Part VII
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
Ernie- I thought the State was responsibie for the infrastructure of this type of installation? I think I'd agree with Greg on this one- The utility can probably do it easier than you. Of course if your getting paid to do it that's a diferent story. Keep me posted.
_________________________
George Little
Top
#92871 - 04/15/05 08:27 AM Re: Recreational Vehicle Parks (551) Part VII
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
I imagine the "park" he is talking about is a privately owned RV park. I did several of these that were state owned when I was inspecting. When you actually put pen to paper the size of wire you need at 240v is mind boggling. Most of these new RVs have 50a cords on them and they can use almost every stinking amp of that. Some have 2 big HVAC systems on the roof and every electrical doodad a person would have at home. The parks were originally wired for campers who just wanted a NEMA 5-15 to run a fan, a light and maybe a TV. The state came to the conclusion the only way they could effectivly cover the distances involved was with MV and they deferred to the utility to own that equipment.
_________________________
Greg Fretwell
Top

Member Spotlight
Member Since: 01/22/05
Posts: 5316
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 95 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals