The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Today at 02:39 AM
Photo Upload Tutorial
by DanK
Yesterday at 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
2 registered (Radar, LongRunner), 224 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#92846 - 04/13/05 07:29 PM outlets
jmcelectric Offline
Member

Registered: 01/20/04
Posts: 16
can 15a rec. be wired to a 20a circuit using the feed thru screws on the rec.? or would you have to splice conductors so there is no more than one wire on device?

Top
2014 / 2011 NEC & Related Books and Study Guides
#92847 - 04/14/05 04:58 AM Re: outlets
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Only the grounded conductor and then only if it is part of a multiwire branch circuit. 300.13(B). If it were my job I'd pigtail both of the circuit conductors because it's a more reliable job. But, code is minimum and that's what all I can ask for as an inspector.
_________________________
George Little

Top
#92848 - 04/14/05 06:15 AM Re: outlets
Ryan_J Offline
Moderator

Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
 Quote:
can 15a rec. be wired to a 20a circuit using the feed thru screws on the rec.?


Yes
_________________________
Ryan Jackson,
Salt Lake City

Top
#92849 - 04/14/05 12:19 PM Re: outlets
Steve Miller Offline
Member

Registered: 08/30/01
Posts: 322
Loc: Loudoun Cty, VA
Gee Ryan ... a one word answer. You must not have had your morning coffee

Top
#92850 - 04/27/05 12:08 AM Re: outlets
Larry Fine Offline
Member

Registered: 02/18/05
Posts: 684
Loc: Richmond, VA
The answer is definitely yes. The neutral should be pigtailed if it's part of a multi-wire circuit, unless the breaker handles are tied together.

The only difference between 15- and 20-amp receptacles of the same grade is the 20-amp-plug rejection of the 15-amp receptacle.

In other words, the slot shape is the only difference; the internals are the same. Ever notice that 15-amp GFCI receptacles are feed-thru rated for 20 amps?
_________________________
Larry Fine
Fine Electric Co.
fineelectricco.com

Top
#92851 - 04/27/05 04:47 AM Re: outlets
kd Offline
Member

Registered: 12/14/04
Posts: 51
#12 wire will not fit in the stab-in slot on a 15 amp receptacle. It is Code legal to install 15 amp receptacles on a 20 amp circuit if there is more than one receptacle on the circuit--if only one receptacle (or one duplex) then it must be 20 amp rating. Use the screws to attach the wire. Do not pigtail #14 wire on a 20 amp circuit. As for multi-wire circuits, always splice the neutral(solid neutral) whether the handles are tied together or not. It is not required to tie the handles--but I believe it should be required. 20 A receptacles have no stab-in slots. Usually the blade holding hardware is stronger. On 20 A circuits, I pigtail hot, neutral, and ground in each box it speeds up the finish electridal.

Top
#92852 - 04/29/05 06:38 PM Re: outlets
Larry Fine Offline
Member

Registered: 02/18/05
Posts: 684
Loc: Richmond, VA
210.4 Multiwire Branch Circuits.
(C) Line-to-Neutral Loads. Multiwire branch circuits shall supply only line-to-neutral loads.
Exception No. 1: A multiwire branch circuit that supplies only one utilization equipment.
Exception No. 2: Where all ungrounded conductors of the multiwire branch circuit are opened simultaneously by the branch-circuit overcurrent device.


210.21 Outlet Devices.
Outlet devices shall have an ampere rating that is not less than the load to be served and shall comply with 210.21(A) and (B).
(B) Receptacles.
(1) Single Receptacle on an Individual Branch Circuit. A single receptacle installed on an individual branch circuit shall have an ampere rating not less than that of the branch circuit.


ARTICLE 100 Definitions
Receptacle. A receptacle is a contact device installed at the outlet for the connection of an attachment plug. A single receptacle is a single contact device with no other contact device on the same yoke. A multiple receptacle is two or more contact devices on the same yoke.


300.13 Mechanical and Electrical Continuity — Conductors.
(B) Device Removal. In multiwire branch circuits, the continuity of a grounded conductor shall not depend on device connections such as lampholders, receptacles, and so forth, where the removal of such devices would interrupt the continuity.

[This message has been edited by Larry Fine (edited 04-29-2005).]

[This message has been edited by Larry Fine (edited 04-29-2005).]
_________________________
Larry Fine
Fine Electric Co.
fineelectricco.com

Top
#92853 - 04/30/05 01:55 AM Re: outlets
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Larry

Handle ties or not 300.13(B) requires the pig tailing of the neutral.

The exception you highlighted, 210.4(C)Exception No. 2 has no influence on the 300.13(B) requirement to pigtail the grounded conductor.

Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#92854 - 04/30/05 11:37 AM Re: outlets
Larry Fine Offline
Member

Registered: 02/18/05
Posts: 684
Loc: Richmond, VA
You're absolutely correct. My apologies.
_________________________
Larry Fine
Fine Electric Co.
fineelectricco.com

Top
#92855 - 04/30/05 11:54 AM Re: outlets
Ryan_J Offline
Moderator

Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
 Quote:
Gee Ryan ... a one word answer. You must not have had your morning coffee


Yeah...you got me there!
_________________________
Ryan Jackson,
Salt Lake City

Top