#92846 - 04/13/05 07:29 PM outlets
jmcelectric Offline
Member
Registered: 01/20/04
Posts: 16
can 15a rec. be wired to a 20a circuit using the feed thru screws on the rec.? or would you have to splice conductors so there is no more than one wire on device?
Top
2017 / 2014 NEC & Related Books and Study Guides
#92847 - 04/14/05 04:58 AM Re: outlets
George Little Offline
Member
Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Only the grounded conductor and then only if it is part of a multiwire branch circuit. 300.13(B). If it were my job I'd pigtail both of the circuit conductors because it's a more reliable job. But, code is minimum and that's what all I can ask for as an inspector.
_________________________
George Little
Top
#92848 - 04/14/05 06:15 AM Re: outlets
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
Quote:
can 15a rec. be wired to a 20a circuit using the feed thru screws on the rec.?


Yes
_________________________
Ryan Jackson,
Salt Lake City
Top
#92849 - 04/14/05 12:19 PM Re: outlets
Steve Miller Offline
Member
Registered: 08/30/01
Posts: 322
Loc: Loudoun Cty, VA
Gee Ryan ... a one word answer. You must not have had your morning coffee
Top
#92850 - 04/27/05 12:08 AM Re: outlets
Larry Fine Offline
Member
Registered: 02/18/05
Posts: 684
Loc: Richmond, VA
The answer is definitely yes. The neutral should be pigtailed if it's part of a multi-wire circuit, unless the breaker handles are tied together.

The only difference between 15- and 20-amp receptacles of the same grade is the 20-amp-plug rejection of the 15-amp receptacle.

In other words, the slot shape is the only difference; the internals are the same. Ever notice that 15-amp GFCI receptacles are feed-thru rated for 20 amps?
_________________________
Larry Fine
Fine Electric Co.
fineelectricco.com
Top
#92851 - 04/27/05 04:47 AM Re: outlets
kd Offline
Member
Registered: 12/14/04
Posts: 51
#12 wire will not fit in the stab-in slot on a 15 amp receptacle. It is Code legal to install 15 amp receptacles on a 20 amp circuit if there is more than one receptacle on the circuit--if only one receptacle (or one duplex) then it must be 20 amp rating. Use the screws to attach the wire. Do not pigtail #14 wire on a 20 amp circuit. As for multi-wire circuits, always splice the neutral(solid neutral) whether the handles are tied together or not. It is not required to tie the handles--but I believe it should be required. 20 A receptacles have no stab-in slots. Usually the blade holding hardware is stronger. On 20 A circuits, I pigtail hot, neutral, and ground in each box it speeds up the finish electridal.
Top
#92852 - 04/29/05 06:38 PM Re: outlets
Larry Fine Offline
Member
Registered: 02/18/05
Posts: 684
Loc: Richmond, VA
210.4 Multiwire Branch Circuits.
(C) Line-to-Neutral Loads. Multiwire branch circuits shall supply only line-to-neutral loads.
Exception No. 1: A multiwire branch circuit that supplies only one utilization equipment.
Exception No. 2: Where all ungrounded conductors of the multiwire branch circuit are opened simultaneously by the branch-circuit overcurrent device.


210.21 Outlet Devices.
Outlet devices shall have an ampere rating that is not less than the load to be served and shall comply with 210.21(A) and (B).
(B) Receptacles.
(1) Single Receptacle on an Individual Branch Circuit. A single receptacle installed on an individual branch circuit shall have an ampere rating not less than that of the branch circuit.


ARTICLE 100 Definitions
Receptacle. A receptacle is a contact device installed at the outlet for the connection of an attachment plug. A single receptacle is a single contact device with no other contact device on the same yoke. A multiple receptacle is two or more contact devices on the same yoke.


300.13 Mechanical and Electrical Continuity — Conductors.
(B) Device Removal. In multiwire branch circuits, the continuity of a grounded conductor shall not depend on device connections such as lampholders, receptacles, and so forth, where the removal of such devices would interrupt the continuity.

[This message has been edited by Larry Fine (edited 04-29-2005).]

[This message has been edited by Larry Fine (edited 04-29-2005).]
_________________________
Larry Fine
Fine Electric Co.
fineelectricco.com
Top
#92853 - 04/30/05 01:55 AM Re: outlets
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Larry

Handle ties or not 300.13(B) requires the pig tailing of the neutral.

The exception you highlighted, 210.4(C)Exception No. 2 has no influence on the 300.13(B) requirement to pigtail the grounded conductor.

Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#92854 - 04/30/05 11:37 AM Re: outlets
Larry Fine Offline
Member
Registered: 02/18/05
Posts: 684
Loc: Richmond, VA
You're absolutely correct. My apologies.
_________________________
Larry Fine
Fine Electric Co.
fineelectricco.com
Top
#92855 - 04/30/05 11:54 AM Re: outlets
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
Quote:
Gee Ryan ... a one word answer. You must not have had your morning coffee


Yeah...you got me there!
_________________________
Ryan Jackson,
Salt Lake City
Top
Page 1 of 2 1 2 >

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Looking for older post
by sparkyinak
Today at 12:27 AM
License exam
by TRUE POWER
Yesterday at 11:33 PM
Members: Non-Members: Did you know?
by Admin
Yesterday at 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM

Who's Online
0 registered (), 69 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Tom
Tom
Member Since: 01/01/01
Posts: 1069

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals