The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Safety at heights?
by gfretwell
Today at 02:19 AM
Looking for older post
by Trumpy
Today at 01:04 AM
Last time to chat here
by Trumpy
Yesterday at 11:41 PM
Unsafe Situations
by Trumpy
Yesterday at 09:46 PM
Webmaster > Admin
by Trumpy
Yesterday at 08:29 PM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
Admin 35
HotLine1 20
Trumpy 19
Ruben Rocha 17
gfretwell 16
Who's Online
1 registered (Ruben Rocha), 157 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#92728 - 04/05/05 06:27 AM How to figure conduit size
Bill39 Offline
Member

Registered: 11/28/01
Posts: 77
Loc: Indianapolis, IN, USA
I need to figure the proper conduit size for a group of communication cables. These are 3 diffent size cables and I have the OD of each. There will be a mixture of each in several conduits.

Where in the NEC (or elsewhere)do I find this? In the old codebooks I thought there were examples but I'm having trouble finding it in the new one.

Thanks in advance for your replies.

Top
2017 / 2014 NEC & Related Books and Study Guides
#92729 - 04/05/05 07:56 AM Re: How to figure conduit size
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
I'm looking at Chapter 9 Notes to Table 1 note #5 and I would calculate the area of your cables and abide by the percentages in Table 1.

Another item: Note #9 might impact on your measurements.

[This message has been edited by George Little (edited 04-05-2005).]
_________________________
George Little

Top
#92730 - 04/05/05 09:03 AM Re: How to figure conduit size
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
ODxODx.7854 = sq. inch of cables.

Example Cad 5 =.215OD
.215 X .215 X .7854 = .0363051

#12 THHN OD = .111
.111 X .111 X .7854 = 0096769

When you got a mixture of Cables and only know ID use this then go to conduit fill charts.

Top