The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Correct rotation, wrong sequence
by Potseal
12/10/16 03:14 PM
Industrail Control Panel bonding per 409.108
by sparkyinak
12/09/16 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 12
HotLine1 10
Potseal 9
sparkyinak 8
Texas_Ranger 8
Who's Online
1 registered (sparkyinak), 207 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#92718 - 04/04/05 07:27 PM GFP and Generators
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Does the sensor for the generator/transfer get installed on the load or line side of a 2000a. 480v. GFP Service. The issue is, if the GFP trips should the generator start?
_________________________
George Little

Top
2014 / 2011 NEC & Related Books and Study Guides
#92719 - 04/08/05 12:13 PM Re: GFP and Generators
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6805
Loc: Brick, NJ USA
George:
You pose an interesting scenario....
Thinking about it, I would venture a "guess" (at this point) that the line side wins. Again, that's MHO, and I will bring this up with a few other AHJ's.

Where's the xfr switch connected line or load of the MCB?? Is the gen 480??

OK, put it on the load side, get a GF, MCB trips; gen starts. Put it on the line side, get a GF, gen does not start.

This will be a good debate!

Added:
OK, purpose of gen is to provide power during a utility failure; correct?
That thought said, a internal GF is NOT a utility failure, although the results are the same (darkness). I'm sticking with a LINE side reference point at this time.

John

[This message has been edited by HotLine1 (edited 04-08-2005).]
_________________________
John

Top
#92720 - 04/08/05 12:25 PM Re: GFP and Generators
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
I would think you would want (be required) to have the generator take over.

The generator will have it's own GFP if over 1200 amps so it will 'take care of itself' if the ground fault is in the emergency system and is still present.

A fault in the 'normal' power distribution systems should not disable the emergency egress lighting.

JMO, Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#92721 - 04/08/05 01:06 PM Re: GFP and Generators
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Hotline1- I think I'd agree with you. Utility failure and generator takes over.

Story behind the question. - We had a bad electrical fire in a building near me and the utility main let go. There was a 480v. GFP service and the GFP never tripped. The generator started and kept the fire going. No GFP on the generator. Fire would have been less damaging if the generator would have had GFP. Fire deptartment had to shut the generator down and the sprinklers in the equipment room put out the fire. Point here is, if the GFP trips on the main and the low volt sensors on the transfer switch are on the line side of the main the generator probably won't feed the fire. I guess it's a crap shoot either way. Can't find anything in NFPA 70 on this point.

[This message has been edited by George Little (edited 04-08-2005).]
_________________________
George Little

Top
#92722 - 04/10/05 06:30 AM Re: GFP and Generators
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Iwire- look at 701.17 and we see that the alternate source is not required to have GFP and that's what is bothering me.
_________________________
George Little

Top
#92723 - 04/10/05 06:53 AM Re: GFP and Generators
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
I assumed article 700 which would bring us to 700.26.

Regardless, my feeling is it is more important to provide emergency egress lighting then to be concerned with generator promoting the fire.

I look at this the same way as the fire pump rules, let it run till it melts.

JMO, Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#92724 - 04/10/05 10:12 AM Re: GFP and Generators
shortcircuit Offline
Member

Registered: 06/27/04
Posts: 608
Loc: massachusetts
How about a few more details George Little...

1)What was the purpose of the building?
2)Was there just the one 2000amp service to the building?
3)Did the generator backfeed the whole 2000amp service?
4)How old was the electric installation in the building?

Iwire, normal power or generator power, any emergency lighting wall packs and exit signs for egress have battery backup...right

shortcircuit

Top
#92725 - 04/10/05 10:23 AM Re: GFP and Generators
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
ShortC

 Quote:
Iwire, normal power or generator power, any emergency lighting wall packs and exit signs for egress have battery backup...right


Unfortantly no, that is not required.

IMO what you describe is good design.

When the utility drops you can be in darkness for up to 10 seconds until the generator comes on line.

To be clear here, if you have a building with a true Article 700 emergency system powered from a generator there is no requirement to have battery back up of the egress lighting.

Typically the emergency lighting in a building with a generator is the same lighting fixtures used for general illumination.

If you have 2 x 4 troughers lighting an area some of them will be fed from the emergency system.

If you do this in an area with HID lighting you must provide lighting that will cover the time for the lamps to cool and re strike.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#92726 - 04/10/05 01:39 PM Re: GFP and Generators
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
The building was a place of assembly and the generator did not have GFP. I'm not sure exactly what was fed from the generator or if it fed the emergency lighting. The fact that it didn't have GFP may or may not be good. It's not required and I wonder if the fact that it could have been feeding emergency light is why they didn't have GFP. I don't have any more information on this at this time. I wasn't the inspector at the scene and there will be tons of litagation I'm sure. I agree with Bob about the good design attitude but good design cost money and I can only enforce code.
_________________________
George Little

Top
#92727 - 04/12/05 03:31 PM Re: GFP and Generators
tdhorne Offline
Member

Registered: 03/22/01
Posts: 344
Loc: Maryland, USA
 Quote:
I assumed article 700 which would bring us to 700.26.

Regardless, my feeling is it is more important to provide emergency egress lighting then to be concerned with generator promoting the fire.

I look at this the same way as the fire pump rules, let it run till it melts.

JMO, Bob


As a firefighter rather than as an electrician I would agree with Iwire on this one. Having lighting during the evacuation of a public assembly is far more important than limiting the damage to the electrical installation.
--
Tom Horne
_________________________
Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison

Top