The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Safety at heights?
by HotLine1
Yesterday at 08:51 PM
International Wire Colour Codes
by Texas_Ranger
Yesterday at 03:29 PM
Looking for older post
by Texas_Ranger
Yesterday at 03:22 PM
Last time to chat here
by Trumpy
01/20/17 11:41 PM
Unsafe Situations
by Trumpy
01/20/17 09:46 PM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
Admin 35
HotLine1 21
Ruben Rocha 17
gfretwell 16
Trumpy 15
Who's Online
0 registered (), 66 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#92557 - 03/24/05 07:51 AM Article 392 Cable tray Fill
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
Article 392.12 & 392.13
392.12 gives impression cable tray must be sized Min. by the width of all cables laying side by side. 750 unshielded 5 kv cable =1.62. 1.62 x18= 29.16 inches = 30 " tray min.
392.13 (b) deals with Ampacity of single conductors in tray.
#1 laying side by side Copper 75% of table 310.69 , Covered (6 ft or more)70% 310.69

#2 Single row space of conductor in between =100% of table 310.69

#3 Conductors bundled (3 in a bundle A-B-C-phase) and a space of 2.15 x conductor size between = 310.67 100%.

Question Can bundles be put side by side???
Can try be Sized by width of bundles side by side? 1.62x2=3.24x 6(bundles)=19.44 tray say 24Inch?? ( I feel No)

Ampacity of bundled conductors side by side (If allowed) cause the code does not reference a side by side bundled arraigment.

I feel the Org. 30 inch and bunded with spacing is proper . Looking for Imput .

Yoopersup

Top
2017 / 2014 NEC & Related Books and Study Guides
#92558 - 03/24/05 10:00 AM Re: Article 392 Cable tray Fill
Joe Tedesco Offline
Member

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
Here's a link to the Cable Tray Institute, they may have an answer to the questions you raise.
http://www.cabletrays.com/
_________________________
Joe Tedesco, NEC Consultant