The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by HotLine1
Today at 09:39 AM
International Wire Colour Codes
by Texas_Ranger
Yesterday at 08:24 AM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 12
HotLine1 7
renosteinke 6
ghost307 5
Potseal 4
Who's Online
1 registered (Tjia1981), 209 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#92557 - 03/24/05 07:51 AM Article 392 Cable tray Fill
Yoopersup Offline

Registered: 03/04/03
Posts: 826
Loc: Michigan
Article 392.12 & 392.13
392.12 gives impression cable tray must be sized Min. by the width of all cables laying side by side. 750 unshielded 5 kv cable =1.62. 1.62 x18= 29.16 inches = 30 " tray min.
392.13 (b) deals with Ampacity of single conductors in tray.
#1 laying side by side Copper 75% of table 310.69 , Covered (6 ft or more)70% 310.69

#2 Single row space of conductor in between =100% of table 310.69

#3 Conductors bundled (3 in a bundle A-B-C-phase) and a space of 2.15 x conductor size between = 310.67 100%.

Question Can bundles be put side by side???
Can try be Sized by width of bundles side by side? 1.62x2=3.24x 6(bundles)=19.44 tray say 24Inch?? ( I feel No)

Ampacity of bundled conductors side by side (If allowed) cause the code does not reference a side by side bundled arraigment.

I feel the Org. 30 inch and bunded with spacing is proper . Looking for Imput .


2014 / 2011 NEC & Related Books and Study Guides
#92558 - 03/24/05 10:00 AM Re: Article 392 Cable tray Fill
Joe Tedesco Offline

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
Here's a link to the Cable Tray Institute, they may have an answer to the questions you raise.