#92545 - 03/22/05 07:46 PM AFCI protection of switches
BigB Offline
Member
Registered: 03/31/04
Posts: 719
Loc: Tucson, AZ USA
I realize AFCI protection is required at all bedroom outlets including the smoke but I have a situation where the whole bedroom is on one circuit, then there is a two gang box by the patio door. In this two gang box there is a three way for the bedroom light and a four way which switches the patio lighting which is on a different circuit. Would this be a violation? Should the patio circuit now also be AFCI protected because this one switch's wiring enters the bedroom 2 gang?

By the way didn't there used to be an AFCI forum?
Top
2017 / 2014 NEC & Related Books and Study Guides
#92546 - 03/23/05 11:42 AM Re: AFCI protection of switches
pdh Offline
Member
Registered: 01/20/05
Posts: 354
Quote:
210.12(B) Dwelling Unit Bedrooms. All 120-volt, single-phase, 15- and 20-ampere branch circuits supplying outlets installed in dwelling unit bedrooms shall be protected ...


What I read here is that this is protection required of the circuit itself (not of just the outlet), if the circuit is supplying an outlet installed in a bedroom. So is your 4-way switch considered an outlet? Is the patio light considered installed in the bedroom?
Top
#92547 - 03/23/05 04:24 PM Re: AFCI protection of switches
HLCbuild Offline
Member
Registered: 12/05/04
Posts: 209
Loc: Herndon,Va USA
The way I see it is a switch is not an outlet by the definitions (Article 100) in the NEC. An outlet is "a point on the wiring system at which current is taken to supply utilization equipment". A switch is "a device...capable of interrupting its rated current at its rated voltage". It is not the point at which current is taken to supply utilization equipment...IMO.
Harold
Top
#92548 - 03/23/05 04:34 PM Re: AFCI protection of switches
Roger Offline
Member
Registered: 05/18/02
Posts: 1716
Loc: N.C.
I agree, the switch (which is not an outlet) for a circuit serving outlets outside of the bedroom would not be an issue.

This can be expanded into allowing 125v non AFCI 15 and 20 amp breakers in a panel or enclosure to be installed in the bedroom.

Roger

[This message has been edited by Roger (edited 03-23-2005).]
Top
#92549 - 03/23/05 07:00 PM Re: AFCI protection of switches
BigB Offline
Member
Registered: 03/31/04
Posts: 719
Loc: Tucson, AZ USA
Thanks a heap guys.
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 55 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals