The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
sparkyinak 9
Texas_Ranger 8
Potseal 6
Who's Online
0 registered (), 78 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#92486 - 03/17/05 05:11 PM water pipe bonding
sid123456 Offline
Member

Registered: 01/18/05
Posts: 72
Loc: Florida
what is the requirement (wire size) for bonding the copper water pipe when it comes in as a poly pipeand changes over to copper?

Top
2014 / 2011 NEC & Related Books and Study Guides
#92487 - 03/17/05 06:25 PM Re: water pipe bonding
shortcircuit Offline
Member

Registered: 06/27/04
Posts: 608
Loc: massachusetts
Follow the rules of table 250.66 as instructed by 250.104(A)(1)2005NEC

shortcircuit