#92486 - 03/17/05 05:11 PM water pipe bonding
sid123456 Offline
Member
Registered: 01/18/05
Posts: 71
Loc: Florida
what is the requirement (wire size) for bonding the copper water pipe when it comes in as a poly pipeand changes over to copper?
Top
2017 / 2014 NEC & Related Books and Study Guides
#92487 - 03/17/05 06:25 PM Re: water pipe bonding
shortcircuit Offline
Member
Registered: 06/27/04
Posts: 608
Loc: massachusetts
Follow the rules of table 250.66 as instructed by 250.104(A)(1)2005NEC

shortcircuit
Top