#92414 - 03/16/05 08:00 AM Generator Disconnect Switch in Building
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 822
Loc: Michigan
Generator remote from building ,has disconnect switch on it. Runs to building inside to Transfer Switch. Is a Additional Disconnect switch Required per Article 225.As the Generator feeders enter the building and before the Transfer switch?
Top
2017 / 2014 NEC & Related Books and Study Guides
#92415 - 03/16/05 08:26 AM Re: Generator Disconnect Switch in Building
shortcircuit Offline
Member
Registered: 06/27/04
Posts: 608
Loc: massachusetts
whatsup yoopersup...I say yes to your question, and it must be suitable for service equipment.

Unless the transfer equipment meets the qualifications of Article 225...

shortcircuit
Top
#92416 - 03/16/05 08:32 AM Re: Generator Disconnect Switch in Building
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 822
Loc: Michigan
Found the Answer ,700.12B(6)Was added in the 2002 Code. take a look.
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (ComputerWizKid), 72 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals