The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
1 registered (gfretwell), 313 Guests and 3 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#92412 - 03/16/05 07:26 AM dishwasher plug?
tomselectrc Offline

Registered: 03/14/04
Posts: 50
Loc: warren mi us
I have been wiring my dishwasher circuts in the sink base cabnit where the diposal plugs in at. I use a 2pole breaker on that plug. I did this as a disconnet for service would be close. Also it is easy for the plummer to plug in. I was wrote a violation that i could not do this under 400.8 (3) that the cord had to be in same void. Any thoughts?

2014 / 2011 NEC & Related Books and Study Guides
#92413 - 03/16/05 09:28 AM Re: dishwasher plug?
caselec Offline

Registered: 04/14/02
Posts: 557
Loc: San Jose, CA
400.8 Doesn’t say anything about running the cord through cabinets. Ask the inspector to read 422.16(B)(2)(4)