ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

Topic Options
Rate This Topic
#92369 - 03/14/05 06:54 PM Breaker size for 30 hp motor
sparkync Offline
Member
Registered: 10/17/02
Posts: 812
Loc: NC
I must be missing something. When I calculate a 30 hp. motor on 460 volts @ 40 amps, using an inverse time breaker, I get:
40 amps X 250 % = 100 amps. I just looked in my "Uglies Electrical References" book, and they calculate it as being a 70 amp. breaker. Any idea what's going on. I have a 400 amp. panel I'm getting ready to order, and I have to have the breaker sizes ready to order it. I don't want to order the wrong size breakers Pretty expensive mistake. Does not 430-52 allow me to go up to the next higher rated breaker if my calculations do not correspond to a standard size?? In this particular case, 100 amp. is a standard size, but I have other ones that will not be. I figure " Ugly is probably right, but where am I going wrong?? I can't afford to calculate this job wrong. Thanks again... Steve
Top
2017 / 2014 NEC & Related Books and Study Guides
#92370 - 03/14/05 08:29 PM Re: Breaker size for 30 hp motor
Bob Offline
Member
Registered: 02/05/02
Posts: 182
Loc: Mobile, AL, USA
It looks like your caculations are correct.
The 100 amp is the max size breaker you can use. You may not go up the the next size.
You may go to an 80 amp breaker if it will
allow the motor to start.
i don't know why Uglys would list a 70 amp.
That seems to be too small.
Top
#92371 - 03/15/05 04:34 AM Re: Breaker size for 30 hp motor
Electric Ian Offline
Member
Registered: 02/10/04
Posts: 133
Loc: MA, USA
430.52(C)(1) Exception 1 allows going to the next higher size the way I read it.

Exception No. 1: Where the values for branch-circuit short-circuit and ground-fault protective devices determined by Table 430.52 do not correspond to the standard sizes or ratings of fuses, nonadjustable circuit breakers,thermal protective devices, or possible settings of adjustable circuit breakers, a higher size, rating, or possible setting that does not exceed the next higher standard ampere rating shall be permitted.
Top
#92372 - 03/15/05 06:27 AM Re: Breaker size for 30 hp motor
rad74ss Offline
Member
Registered: 04/19/04
Posts: 156
Loc: Pryor, OK USA
Table 430-152 lists the maximum setting of 250%. This can be changed per 430-52(c)(1)(c)to 400% for loads of 100A or less. I think Uglies is looking at the breaker as disconnecting means per 430-110. This gives a minimum 115%. Where I work we use mimimum 150% on motor circuit breakers with a maximum of 400%. I think the only other consideration would be given to the locked rotor amp rating.

Still, 150% of 40 would be a 60 amp breaker. Are they using 175%? I can't think of any reason in particular they would use that. Edit from here, I looked at the wrong column.

[This message has been edited by rad74ss (edited 03-16-2005).]
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6778
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 53 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals