#92345 - 03/14/05 11:58 AM Neutral Counted As Current Carrying
mustangelectric Offline
Member
Registered: 02/08/04
Posts: 494
Loc: Bentonville, AR
If a circuit supplies a fluorescent, mercury or metal halide do the neutrals still have to be counted as current carrying? This neutral will carry a third harmonic.

Thanks for any replies

Greg
_________________________
Electricity has no respect for ignorance!
Top
2017 / 2014 NEC & Related Books and Study Guides
#92346 - 03/14/05 12:29 PM Re: Neutral Counted As Current Carrying
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1374
Loc: West Jordan, Utah, USA
Yes, any non-linear(harmonic) load creates a current carrying nuetral.
_________________________
Ryan Jackson,
Salt Lake City
Top
#92347 - 03/14/05 12:35 PM Re: Neutral Counted As Current Carrying
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
Only on 3 phase systems.
Don
_________________________
Don(resqcapt19)
Top
#92348 - 03/14/05 02:09 PM Re: Neutral Counted As Current Carrying
Joe Tedesco Offline
Member
Registered: 10/07/00
Posts: 2749
Loc: Boston, Massachusetts USA
... and only when that nonlinear load is the major portion (over 50%) ....

See the 2005 NEC .....

Nonlinear Load. A load where the wave shape of the steady-state current does not follow the wave shape of the applied voltage.

Article 310

(c) On a 4-wire, 3-phase wye circuit where the major portion of the load consists of nonlinear loads, harmonic currents are present in the neutral conductor; the neutral shall therefore be considered a current-carrying conductor.
FPN: Electronic equipment, electronic/electric-discharge lighting, adjustable-speed drive systems, and similar equipment may be nonlinear loads.
_________________________
Joe Tedesco, NEC Consultant
Top
#92349 - 03/14/05 07:58 PM Re: Neutral Counted As Current Carrying
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9038
Loc: Estero,Fl,usa
You can still induce out of phase currents in a single phase neutral (multiwire circuit) but you won't get the overload effect you get in 3 phase. It can still make measurememnts not balance if your meter isn't true RMS.
_________________________
Greg Fretwell
Top

Member Spotlight
Member Since: 01/22/05
Posts: 5316
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 56 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals