The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
sparkyinak 9
Texas_Ranger 8
Potseal 6
Who's Online
0 registered (), 194 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#92256 - 03/10/05 02:12 PM 50A range recep on 40A OCPD & wire?
royta Offline
Member

Registered: 09/03/04
Posts: 136
Loc: CA
I know that you can't use a 20A recep on a 15A circuit, but can you use a 50A range recep on a 40A circuit, or is does the same rule apply?

Thanks.

Roy

Top
2014 / 2011 NEC & Related Books and Study Guides
#92257 - 03/10/05 02:25 PM Re: 50A range recep on 40A OCPD & wire?
tdhorne Offline
Member

Registered: 03/22/01
Posts: 344
Loc: Maryland, USA
IMS the table in the NEC specifically allows the use of a fifty ampere receptacle on a forty ampere circuit. That is the practical thing to do when the load will be cord and plug connected because there is no source for forty ampere cords and plugs.
--
Tom H
_________________________
Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison

Top
#92258 - 03/10/05 03:02 PM Re: 50A range recep on 40A OCPD & wire?
royta Offline
Member

Registered: 09/03/04
Posts: 136
Loc: CA
That makes sense tdhorne. Thanks.

Roy

Top
#92259 - 03/11/05 11:20 AM Re: 50A range recep on 40A OCPD & wire?
tdhorne Offline
Member

Registered: 03/22/01
Posts: 344
Loc: Maryland, USA
I checked the table and that is the right answer.

The table in question is 210.24. I looked at several list of receptacle patterns, including the ones in the NEC Handbook, without finding one for forty amperes.
--
Tom H
_________________________
Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison