The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
International Wire Colour Codes
by Texas_Ranger
Today at 08:24 AM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
230 or 345 kV transmission lines?
by annemarie1
10/12/16 01:23 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
renosteinke 6
HotLine1 6
ghost307 5
Potseal 4
Who's Online
0 registered (), 198 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#92222 - 03/08/05 09:57 AM Cable Tray fill (392)
Yoopersup Offline

Registered: 03/04/03
Posts: 826
Loc: Michigan
High voltage (4160) single conductors 750 1.43 dia. 3sets of 3 and 6 sets of 3.Only reference for Single conductors on installtion is 392(B)2 which refers you to 392.3(B)(1) . 392.12 Says they can be grouped or bundled . The way 392.12 is written it looks like even thought you bundle them. The tray must be sized as thought they were laying side by side.Am I reading this right??? I know the way there installed affects there Ampacity. Per 392.13(B)

2014 / 2011 NEC & Related Books and Study Guides
#92223 - 03/10/05 06:50 AM Re: Cable Tray fill (392)
eesac Offline
New Member

Registered: 02/25/05
Posts: 8
Loc: california
I read it the same as you, add up all the diameters of each individual cable, bundled or not.

#92224 - 03/12/05 05:02 AM Re: Cable Tray fill (392)
George Little Offline

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Yooper- I'm not sure you are correct or maybe I'm not reading your statment the way you meant it to be read. I think it says that if you want to bundle cables together or if you are using triplex or quadplex you can use them and you should maintain spacing between the bundles equal to the diameter of a single conductor, so the spacing between two bundles of 4/0 would be the equal to the diameter of a single 4/0 conductor. The spacing between the wouldn't have to be equal to the diameter of the bundle. Is that the way you understand it?
George Little