#92218 - 03/07/05 09:47 PM 10 ft tap rule
aldav53 Offline
Member
Registered: 08/22/01
Posts: 545
Loc: Chandler, AZ USA
From what I get from the 10 foot tap rule is that if a sub-panel run in over 10 ft, you have to feed it - breaker protected. Am I wrong?
25ft tap rule? I'll have to check on that one. Any short explanations?
_________________________
The Golden Rule - "The man with the gold makes the rule"
Top
2017 / 2014 NEC & Related Books and Study Guides
#92219 - 03/08/05 08:27 AM Re: 10 ft tap rule
dana1028 Offline
Member
Registered: 01/09/02
Posts: 163
Loc: San Carlos, CA
RE: 10 ft. Tap rule - (you should take a look at 240.21(B) for specifics)....IF the size of your tap conductor is rated at only 1/10 the size of the conductor you are tapping, then yes, you are limited to 10 ft.

However, if you increase the size of your tap conductor so it is sized at 1/3 the ampacity of the conductor you are tapping, then you can increase the distance to 25 ft. [see 240.21 (B)(2)].

If these tap conductors are running on the outside of the building, then you have unlimited length [see 240.21(B)(5)].
Top
#92220 - 03/08/05 11:33 AM Re: 10 ft tap rule
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
Dana- You need to look at that again- If you are in 240 the tap conductor relates to the device on the feeder. In fact conventional wisdom would have us relating to the device on a 10' tap. ie if the device were a 1200a switch the minumum size wire would have to be 120a. 25' tap relates to the "over current device" so if the 1200a switch had 800a fuses, we'd need to be 1/3 of the 800a.

When you go into Art. 430 for motors the taps change slightly.
_________________________
George Little
Top
#92221 - 03/09/05 09:04 AM Re: 10 ft tap rule
dana1028 Offline
Member
Registered: 01/09/02
Posts: 163
Loc: San Carlos, CA
yes - I was trying not to be too wordy or confusing. All conductor ratings have to be protected by a corresponding OCPD...these ratios to value 1/10, 1/3, etc. are detailed in 240.21(B).
Top

Member Spotlight
Member Since: 08/22/05
Posts: 44
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 30 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals