The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
ghost307 7
HotLine1 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 293 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#92201 - 03/07/05 05:19 AM Sizing Equipment Ground
sparkync Offline

Registered: 10/17/02
Posts: 811
Loc: NC
When running motor circuits in conduit, where the breaker size is 250% of the FLA, is there an exception to the rule of sizing the equipment grounding conductor, according to the rating of the OCD in the circuit? For example I have a machine with a total amperage of 39.8 amps X 250% = 99.5 amps which would put me at a 100 amp. breaker. Is the ground wire size for the conduit still a # 8 or am I missing an exception somewhere when dealing with motor circuits.. I have other smaller motor circuit conductors in the conduit also, but this is the largest. Thanks, Steve

2014 / 2011 NEC & Related Books and Study Guides
#92202 - 03/07/05 07:37 AM Re: Sizing Equipment Ground
gfretwell Offline


Registered: 07/20/04
Posts: 9026
Loc: Estero,Fl,usa
250.122(A) General. Copper, aluminum, or copper-clad aluminum equipment grounding conductors of the wire type shall not be smaller than shown in Table 250.122 but shall not be required to be larger than the circuit conductors supplying the equipment.
Greg Fretwell

#92203 - 03/07/05 07:41 AM Re: Sizing Equipment Ground
resqcapt19 Offline

Registered: 11/10/00
Posts: 2209
Loc: IL
If you are using a motor circuit protector or magnetic only breaker for the short circuit and ground fault protection then 250.122(D) lets you size the EGC based on the overload protection rating. In your case, it appears that you are using a thermal magnetic breaker and you must size based on the breaker rating, however as greg pointed out 250.122(A) says the EGC is not required to be larger than the circuit conductors, but that does not change anything for your example as the circuit conductors will be #8 and Table 250.122 calls for a #8 EGC for a 100A OCPD.