#92201 - 03/07/05 05:19 AM Sizing Equipment Ground
sparkync Offline
Member
Registered: 10/17/02
Posts: 812
Loc: NC
When running motor circuits in conduit, where the breaker size is 250% of the FLA, is there an exception to the rule of sizing the equipment grounding conductor, according to the rating of the OCD in the circuit? For example I have a machine with a total amperage of 39.8 amps X 250% = 99.5 amps which would put me at a 100 amp. breaker. Is the ground wire size for the conduit still a # 8 or am I missing an exception somewhere when dealing with motor circuits.. I have other smaller motor circuit conductors in the conduit also, but this is the largest. Thanks, Steve
Top
2017 / 2014 NEC & Related Books and Study Guides
#92202 - 03/07/05 07:37 AM Re: Sizing Equipment Ground
gfretwell Online   content


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
250.122(A) General. Copper, aluminum, or copper-clad aluminum equipment grounding conductors of the wire type shall not be smaller than shown in Table 250.122 but shall not be required to be larger than the circuit conductors supplying the equipment.
_________________________
Greg Fretwell
Top
#92203 - 03/07/05 07:41 AM Re: Sizing Equipment Ground
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
If you are using a motor circuit protector or magnetic only breaker for the short circuit and ground fault protection then 250.122(D) lets you size the EGC based on the overload protection rating. In your case, it appears that you are using a thermal magnetic breaker and you must size based on the breaker rating, however as greg pointed out 250.122(A) says the EGC is not required to be larger than the circuit conductors, but that does not change anything for your example as the circuit conductors will be #8 and Table 250.122 calls for a #8 EGC for a 100A OCPD.
Don
_________________________
Don(resqcapt19)
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (gfretwell), 95 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals