#92171 - 03/03/05 07:40 AM NEC says Riser Rated Cat5 in Residence?
vermonster Offline
Junior Member
Registered: 03/03/05
Posts: 2
Loc: NEK, VT USA
I'm the GC on the renovation of a 1780 post&beam farmhouse.

Currently have some disagreement on the job site. Some feel that because communication wiring is run in the unblocked wall from basement to 2nd floor, riser rated cable is required. Others disagree and state the NEC indicates type CM is always sufficient for single family residential dwellings.

Can somebody point me one way or the other.

As about 50% of the place is already wired in CM, we are hoping this meets the NEC, but will rewire if required.

Thanks

George
Top
2017 / 2014 NEC & Related Books and Study Guides
#92172 - 03/03/05 08:15 AM Re: NEC says Riser Rated Cat5 in Residence?
eesac Offline
New Member
Registered: 02/25/05
Posts: 8
Loc: california
I do not believe you need riser rated cables in residences, see 1999 NEC 800-53-b exception #2, which basically allows CM or CMX cables in one and two family dwellings. The newer NEC will probably read the same.
Top
#92173 - 03/03/05 11:21 AM Re: NEC says Riser Rated Cat5 in Residence?
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9036
Loc: Estero,Fl,usa
NEC 2002 made this positive language
800.53(B) Riser. Cables installed in risers shall comply with 800.53(B)(1), (B)(2), or (B)(3).
...
(3) One- and Two-Family Dwellings. Type CM and CMX cable shall be permitted in one- and two-family dwellings.

NEC2005 moved this to 800.154 but the language didn't change
_________________________
Greg Fretwell
Top
#92174 - 03/03/05 11:57 AM Re: NEC says Riser Rated Cat5 in Residence?
vermonster Offline
Junior Member
Registered: 03/03/05
Posts: 2
Loc: NEK, VT USA
Many thanks. It is quite clear that type CM is sufficient in single family dwellings regardless of whether the space is considered a "riser" or not.

Elsewhere someone had suggested:
725.61(B)(3), since it allows CL2 and CL3 in 1-2 family dwellings and the cable hierarchy allows substitution of type CM where CL2/3 is allowed.

George
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6775
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 55 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals