The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Forum Software Upgrade coming soon...
by HotLine1
01/17/17 03:23 PM
Would ELV branch circuits be a good idea?
by gfretwell
01/17/17 01:26 PM
Why cables look like they do
by Texas_Ranger
01/17/17 12:33 PM
Re: Fabricating Guards out of Lexan?
by ghost307
01/17/17 11:21 AM
100% breakers?
by Texas_Ranger
01/16/17 06:13 AM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
HotLine1 20
Webmaster 15
Trumpy 12
ghost307 12
gfretwell 11
Who's Online
2 registered (HotLine1, frank), 0 Guests and 69 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#92171 - 03/03/05 07:40 AM NEC says Riser Rated Cat5 in Residence?
vermonster Offline
Junior Member

Registered: 03/03/05
Posts: 2
Loc: NEK, VT USA
I'm the GC on the renovation of a 1780 post&beam farmhouse.

Currently have some disagreement on the job site. Some feel that because communication wiring is run in the unblocked wall from basement to 2nd floor, riser rated cable is required. Others disagree and state the NEC indicates type CM is always sufficient for single family residential dwellings.

Can somebody point me one way or the other.

As about 50% of the place is already wired in CM, we are hoping this meets the NEC, but will rewire if required.

Thanks

George

Top
2017 / 2014 NEC & Related Books and Study Guides
#92172 - 03/03/05 08:15 AM Re: NEC says Riser Rated Cat5 in Residence?
eesac Offline
New Member

Registered: 02/25/05
Posts: 8
Loc: california
I do not believe you need riser rated cables in residences, see 1999 NEC 800-53-b exception #2, which basically allows CM or CMX cables in one and two family dwellings. The newer NEC will probably read the same.

Top
#92173 - 03/03/05 11:21 AM Re: NEC says Riser Rated Cat5 in Residence?
gfretwell Offline


Member

Registered: 07/20/04
Posts: 9060
Loc: Estero,Fl,usa
NEC 2002 made this positive language
800.53(B) Riser. Cables installed in risers shall comply with 800.53(B)(1), (B)(2), or (B)(3).
...
(3) One- and Two-Family Dwellings. Type CM and CMX cable shall be permitted in one- and two-family dwellings.

NEC2005 moved this to 800.154 but the language didn't change
_________________________
Greg Fretwell

Top
#92174 - 03/03/05 11:57 AM Re: NEC says Riser Rated Cat5 in Residence?
vermonster Offline
Junior Member

Registered: 03/03/05
Posts: 2
Loc: NEK, VT USA
Many thanks. It is quite clear that type CM is sufficient in single family dwellings regardless of whether the space is considered a "riser" or not.

Elsewhere someone had suggested:
725.61(B)(3), since it allows CL2 and CL3 in 1-2 family dwellings and the cable hierarchy allows substitution of type CM where CL2/3 is allowed.

George

Top