#92160 - 03/02/05 03:56 AM Cold air returns
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
Article 300 section 300.22(C) Exception talks about the wiring in cold air returns as being exempt from complying with the requirement of metallic raceway (short version). I wonder if I understand this correctly in that if NM cable passes through the joist space perpendicular to the air flow, it's code compliant and doesn't need any other consideration. Now, if we decide to install a switch box or a receptacle opening in the CA, we would need a metallic wiring method.
_________________________
George Little
Top
2017 / 2014 NEC & Related Books and Study Guides
#92161 - 03/02/05 05:02 AM Re: Cold air returns
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 822
Loc: Michigan
Yep
That applies to Space used for Environmental Air(300.22c) only. Not Ducts or Plenums(300.22b) as you stated.2002 Handbook NFPA shows a picture example.
Top
#92162 - 03/04/05 08:07 PM Re: Cold air returns
harold endean Offline
Member
Registered: 02/16/02
Posts: 2233
Loc: Boonton, NJ
By careful though, even if our code does allow it, the local building or fire code may not. I would check with the local AHJ on this one. You would hat to have all the work rough-in and then have to change it later on.
Top
#92163 - 03/06/05 08:36 AM Re: Cold air returns
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
Recently, I was working alongside an HVAC guy, and I saw an interesting practice. To make a duct, he simply sheathed the open face of a rafter bay with sheet metal, and sealed the edges. This way, the subfloor above, and the two rafters, formed three sides of the duct.
I believe that this is what the code writers had in mind whan the exception was written into the code- as opposed to, say, someone actually punching holes in a metal duct in order to run their wires.
In other words, I suspect the exception is there for the convenience of the HVAC guy, rather than the electrician- though it also recognises that such a duct would be impossible to "go around."
Top
#92164 - 03/06/05 12:47 PM Re: Cold air returns
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
And I agree with you Reno, Where it get's controversial is when the installer installs outlet boxes or switch boxes in these spaces. I've asked them about that and they offer to install a barrier around the box and thus divorcing the box from the cold air return. Now the mechanical contractor gets upset because the electrical restricts the air flow. You can't win sometimes.
_________________________
George Little
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 48 Guests and 12 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals