The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
1 registered (LongRunner), 221 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#92151 - 02/28/05 07:33 PM utility building ground rod
sparkync Offline
Member

Registered: 10/17/02
Posts: 811
Loc: NC
Can't seem to find the code reference now, but am I correct that even though a 4 wire feeder is run to a detached utility building, a ground rod is still required at the utility building, and the ground wire from the 4 wire feeder, and the ground wire to the new ground rod would go on the same ground bar that is isolated from the neutral bar ? Thanks Steve...

Top
2014 / 2011 NEC & Related Books and Study Guides
#92152 - 02/28/05 07:47 PM Re: utility building ground rod
Speedy Petey Offline
Member

Registered: 08/29/03
Posts: 175
Loc: Upstate, NY
Yes. Any detached structure requires a ground rod. That is any one with a sub-panel.
Your description is also correct.

[This message has been edited by Speedy Petey (edited 02-28-2005).]
_________________________
Speedy Petey

"Anyone who has never made a mistake has never tried anything new." -Albert Einstein

Top
#92153 - 02/28/05 07:52 PM Re: utility building ground rod
shortcircuit Offline
Member

Registered: 06/27/04
Posts: 608
Loc: massachusetts
250.32(A) requires a grounding electrode at the building.If you use a rod electrode and you don't have 25 ohms or less, add one additional electrode as required by 250.56

250.32(B)(1)describes the proper installation arrangement of the EGC and the grounded conductor.(float the neutral)

shortcircuit

Top