The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by ghost307
10/24/16 06:25 AM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 307 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#92147 - 02/28/05 12:07 PM "Boot-leg" ground connections
safetygem Offline

Registered: 01/30/02
Posts: 114
Loc: Ohio, USA
Hey guys (and gals)

What is the correct NEC reference that prohibits a "boot-leg" or "false" ground in a receptacle or other equipment?

Is it 250.142(B) or there a better section?

Thanks in advance for your help!

2014 / 2011 NEC & Related Books and Study Guides
#92148 - 02/28/05 12:43 PM Re: "Boot-leg" ground connections
iwire Offline

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
250.142(B) IMO is enough but you could also look to 250.24(A)(5).

250.24(A)(5) Load-Side Grounding Connections. A grounding connection shall not be made to any grounded circuit conductor on the load side of the service disconnecting means except as otherwise permitted in this article.
Bob Badger
Construction & Maintenance Electrician

#92149 - 02/28/05 01:58 PM Re: "Boot-leg" ground connections
safetygem Offline

Registered: 01/30/02
Posts: 114
Loc: Ohio, USA
Thanks Bob!

#92150 - 03/02/05 05:48 PM Re: "Boot-leg" ground connections
renosteinke Offline
Cat Servant

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
There's a cite worth knowing! I was once at a loss to show where the NEC prohibited using the conduit as a "neutral"....even lost a job over it!