#92134 - 02/26/05 07:58 PM Well casing cap
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
What is the best way to ground/bond the metal cap found on the top of some well casings? Some of the casings (about 50%) are non metallic with a metal cap that could become energized.
_________________________
George Little
Top
2017 / 2014 NEC & Related Books and Study Guides
#92135 - 02/27/05 02:20 AM Re: Well casing cap
shortcircuit Offline
Member
Registered: 06/27/04
Posts: 608
Loc: massachusetts
george...thought we determined that isolated sections of steel need not be bonded

How about braided bonding jumper to the cap terminating to a lug bolted to a tapped 1/4-20 hole in the cover.

It would be better if they used a non-metalic cover with the non-metalic casing IMO.Haven't seen other than metel casings around these parts.

While were on the subject of wells, do the installations that you see have a disconnect at the casing for servicing the pump?

Most of the installations around here have no disconnect at the casing for the pump motor down in the casing and the wiring extends inside the dwelling to a location where a storage tank is, then through the pressure switch, then to the breaker in the service. The breaker at the service being the only disconnect for the installation.Wouldn't this be a violation of 430.102(B)

shortcircuit
Top
#92136 - 02/27/05 05:26 AM Re: Well casing cap
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
430.102(B) Exception (c) uses the word "impracticable" and the definition is impossible, infeasible, unattainable and words like that. So certainly the motor at the bottom of the well fits that exception with respect to locating a disconnect "within sight"
_________________________
George Little
Top
#92137 - 02/27/05 05:32 AM Re: Well casing cap
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
More on well casings: There is concerns about the well cap being energized because there is a splice right there and usually the well driller makes that splice and one can only hope he has the right talent and materials to make a good splice. I'm also hearing that there is a lug on the underside of this cap with a green screw that should be utilized,
_________________________
George Little
Top
#92138 - 02/27/05 08:04 AM Re: Well casing cap
shortcircuit Offline
Member
Registered: 06/27/04
Posts: 608
Loc: massachusetts
IMO...I don't see how locating a disconnect next to the well casing is "impracticable" and would be as close as you can practically get to being in sight of the pump. It would definitely lessen the hazard to service personal from somebody accidentally turning the power on at the panel.

There should be at least provisions to lock the circuit in the open position. Wait a minute...code already says that.

Well to get back on track of your original concern of the metalic well casing cap, I have seen some caps with the ground lug or screw as you describe.

shortcircuit
Top
#92139 - 02/27/05 03:29 PM Re: Well casing cap
gfretwell Online   content


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
I am not sure how they do wells there but here they have an FS box at the well head with a short piece of liquidtite going to the cap. When they "pull" the well they open the splice in that box and disconnect the liquidtite from the box.
I could have installed a disco in the box but I didn't see the point. There is one "in sight" tho in the pump shack about 10' away.




[This message has been edited by gfretwell (edited 02-27-2005).]
_________________________
Greg Fretwell
Top
#92140 - 02/28/05 06:18 PM Re: Well casing cap
harold endean Offline
Member
Registered: 02/16/02
Posts: 2233
Loc: Boonton, NJ
Greg,

They should just use a plastic bonding screw! (LOL) Actually most well casings I see here in NJ have the metal cap with a splice point ( and ground point) right underneath the cap. The well installer "SHOULD" install that ground wire. I will check for it on a Final inspection, but the well installer is usually gine by then. So the GC or EC will have to take care of that problem.
Top
#92141 - 02/28/05 06:42 PM Re: Well casing cap
gfretwell Online   content


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
I never saw an electrical inspector when they punched this well. The well inspector only cared that the well was "producing" and that the old well was capped (poured solid with concrete). If this had been a metal cap there was no reason it couldn't have been bonded to the EGC in the splice box.
_________________________
Greg Fretwell
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 109 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals