Elzappr Offline
Member
Registered: 12/20/01
Posts: 270
Loc: Oregon
Can receptacle outlets be placed under raised floors for power to office equipment?
Top
2017 / 2014 NEC & Related Books and Study Guides
#92114 - 02/26/05 01:15 PM Re: Receptacles under raised floors
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
I would say probably it's red tag time. I say that because a receptacle under the floor would obviously leed to a cord under the floor and now we have trouble with 400.8(5). The exception could be in a computer room, raised floor.
_________________________
George Little
Top
#92115 - 02/26/05 04:03 PM Re: Receptacles under raised floors
gfretwell Online   content


Member
Registered: 07/20/04
Posts: 9037
Loc: Estero,Fl,usa
Even under a computer room raised floor you need plenum rated power cords. There are always going to be receptacles but they will be IEC309s or Russell Stolls, not the usual NEMA 5-15
_________________________
Greg Fretwell
Top
#92116 - 02/26/05 04:36 PM Re: Receptacles under raised floors
Ron Offline
Member
Registered: 03/13/02
Posts: 582
Loc: White Plains, NY
Since a flexible cord can't be below the raised floor, there is no need for a receptacle.
If you are 645 compliant, then its ok if the cord is rated as 'DP'.
Why not place a floor box in the raised floor tile, then all is ok.
_________________________
Ron
Top
#92117 - 02/26/05 06:33 PM Re: Receptacles under raised floors
Elzappr Offline
Member
Registered: 12/20/01
Posts: 270
Loc: Oregon
You all have confirmed my suspicions. What I am dealing with is a 5 story building with cords plugged in regular duplex receptacles under the raised floors. The cords are actually 20' long plug strips. they poke up through bushed holes in the concrete floor tiles. This is not a computer room nor server room situation, just a general office space.
As far as I know, this set-up has never been allowed by code. Right?
Top
#92118 - 02/26/05 06:55 PM Re: Receptacles under raised floors
gfretwell Online   content


Member
Registered: 07/20/04
Posts: 9037
Loc: Estero,Fl,usa
That is not legal, nor is simply converting old computer room space to office space, retaining the raised floor for a "convienient" wiring bay. When computers stopped being an acre of boxes and became a rack they had lots of raised floor real estate. It ends up being an office but they still use the floor for a plenum and they lose all the breaks they got in 645.
_________________________
Greg Fretwell
Top
#92119 - 02/26/05 09:39 PM Re: Receptacles under raised floors
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
Greg, are you sure about this?
Quote:
Even under a computer room raised floor you need plenum rated power cords. There are always going to be receptacles but they will be IEC309s or Russell Stolls, not the usual NEMA 5-15

I thought that the cord and the wiring method to the receptacle were the only issues. please educate me.
_________________________
George Little
Top
#92120 - 02/26/05 09:59 PM Re: Receptacles under raised floors
gfretwell Online   content


Member
Registered: 07/20/04
Posts: 9037
Loc: Estero,Fl,usa
Actually Ron hit the code issue. (listed "DP" cable)
The reason you don't see regular receptacles under the floor is you don't want to crash the system because someone yanked the wrong cable and pulls out a plug to a critical box.
_________________________
Greg Fretwell
Top
#92121 - 02/26/05 10:47 PM Re: Receptacles under raised floors
George Offline
Member
Registered: 02/23/02
Posts: 375
I don't wish to start a fight over the issue, but I don't think it is as clear cut as it could be ...

I can certainly run a standard cord under a table. I can carpet my floor with tables. I can place the recept below table ehight. I can walk on top of the tables and place my furniture on top of the tables.

I used the word "table" where most people would use the word "floor."
Top
#92122 - 02/26/05 11:44 PM Re: Receptacles under raised floors
gfretwell Online   content


Member
Registered: 07/20/04
Posts: 9037
Loc: Estero,Fl,usa
I can call my pool a bathtub but that doesn't mean the AHJ will let me ignore 680.
If your AHJ decides your tables are really a floor you will have to follow the rules about penetrations.
Virtually all computer room floors are plenums, moving environmental air. That is why they have the rules about cable flamability.
There are also recognized office floor duct systems so we want to be sure what we are talking about here.
_________________________
Greg Fretwell
Top
Page 1 of 3 1 2 3 >

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (HotLine1), 111 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals