#92072 - 02/25/05 02:07 AM Physical Protection
shortcircuit Offline
Member
Registered: 06/27/04
Posts: 608
Loc: massachusetts
When isolated (not continuous between enclosures) sections of metal conduit are used for physical protection of nonmetalic cable,like for a floor penetration for exsample, is it required to be grounded?

Code refrences please.

shortcircuit
Top
2017 / 2014 NEC & Related Books and Study Guides
#92073 - 02/25/05 05:52 AM Re: Physical Protection
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
Maybe 250.86 Exception No 2 covers the question.
_________________________
George Little
Top
#92074 - 02/25/05 06:38 AM Re: Physical Protection
shortcircuit Offline
Member
Registered: 06/27/04
Posts: 608
Loc: massachusetts
Thanx George Little...and what determines the distance of "short sections"...

For example could I penetrate a plastered wall with romex, enter 30 feet of EMT with bushings on each end and exit the other end and go back into a wall on the other side of the garage without grounding the EMT at all? The EMT would be provideing physical protection of the romex.

shortcircuit
Top
#92075 - 02/25/05 11:02 AM Re: Physical Protection
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
From a practical sense, the most likely places where a cable could energize the sleeve are the ends, so the length won't change that risk much. If you are talking about the raceway being energized by an unrelated circuit we fall back to the arguments about bonding that steel beam.
(and we don't want to kick that tar baby again)
_________________________
Greg Fretwell
Top
#92076 - 02/25/05 01:21 PM Re: Physical Protection
shortcircuit Offline
Member
Registered: 06/27/04
Posts: 608
Loc: massachusetts
gfretwell...I was not thinking so much about the may become energized from the outside, but was thinking what would happen if this EMT providing physical protection were to become damaged itself from a inadvertent impact of some sort and then becoming energized by the circuit it protects.
Guess that I'm reaching again

shortcircuit
Top
#92077 - 02/25/05 01:47 PM Re: Physical Protection
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
I guess the real question is how you would bond the raceway to the RX without a box to open up the jacket in.
_________________________
Greg Fretwell
Top
#92078 - 02/25/05 04:51 PM Re: Physical Protection
earlydean Offline
Member
Registered: 12/22/03
Posts: 751
Loc: Griswold, CT, USA
The same way we have to bond that steel 90 in the UG service PVC run that isn't 18 inches below grade. With a ground clamp or bushing and a wire to the ground bus in the panel.
_________________________
Earl
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 93 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals