#92058 - 02/23/05 06:04 PM 3 wire range circuit  
gserve  Offline
Member
Joined: Mar 2003
Posts: 92
Has 8/2 romex with a#10 bare ground wire ever been allowed to feed a range receptacle? I saw this installation today in a modular home that is a 1979 and that romex was installed by the manufacturer of the home. Is this not supposed to be a 4 wire circuit? Was this ever allowed in a regular stick built house? All I have seen in my area is SEU used for this purpose and the neutral is bare.Bottom line this is installed and they need to replace the range with a new one. So can this be used with a 3 wire cord with the stove ground link attached to the range and the bare #10 used as the neutral and ground for the circuit? Code references and comments please.


2017 / 2014 NEC & Related Books and Study Guides

#92059 - 03/11/05 01:41 PM Re: 3 wire range circuit  
tdhorne  Offline
Member
Joined: Mar 2001
Posts: 345
Maryland, USA
I could be mistaken but I believe that the present rules for existing dryer circuits echo the old rules. I don't believe that a bare neutral was ever allowed in any cable other than type SE. The key to your mystery may well be that it is a manufactured building. One of the big arguments against manufactured buildings was that they were not built to the same standard as site built structures. One of the ways that this worked out in practice was the use of wiring techniques that would never have passed inspection under the US NEC.

It is worth noting that in trailer chassis mounted units the three wire circuits for ranges and clothes dryers was never an accepted practice. Modular buildings that would be placed without the transport chassis were a different story all together.

250.140 Frames of Ranges and Clothes Dryers.
This section shall apply to existing branch-circuit installations only. New branch-circuit installations shall comply with 250.134 and 250.138. Frames of electric ranges, wall-mounted ovens, counter-mounted cooking units, clothes dryers, and outlet or junction boxes that are part of the circuit for these appliances shall be grounded in the manner specified by 250.134 or 250.138; or, except for mobile homes and recreational vehicles, shall be permitted to be grounded to the grounded circuit conductor if all the following conditions are met.
(1) The supply circuit is 120/240-volt, single-phase, 3-wire; or 208Y/120-volt derived from a 3-phase, 4-wire, wye-connected system.
(2) The grounded conductor is not smaller than 10 AWG copper or 8 AWG aluminum.
(3) The grounded conductor is insulated, or the grounded conductor is uninsulated and part of a Type SE service-entrance cable and the branch circuit originates at the service equipment.
(4) Grounding contacts of receptacles furnished as part of the equipment are bonded to the equipment.
--
Tom H


Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison


Member Spotlight
dougwells
dougwells
kamloops BC Canada
Posts: 1,137
Joined: May 2003
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.008s Queries: 14 (0.002s) Memory: 0.7431 MB (Peak: 0.8574 MB) Zlib enabled. Server Time: 2017-03-24 06:15:31 UTC