The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
Texas_Ranger 8
Trumpy 8
sparkyinak 7
Who's Online
1 registered (LongRunner), 90 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 5 1 2 3 4 5 >
Topic Options
Rate This Topic
#91867 - 02/12/05 06:46 AM Structural Steel
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
At what point do we consider the need to bond structural steel. Does a steel I Beam supported by steel post setting on concrete need to be bonded?
_________________________
George Little

Top
2014 / 2011 NEC & Related Books and Study Guides
#91868 - 02/12/05 07:23 AM Re: Structural Steel
George Offline
Member

Registered: 02/23/02
Posts: 380
It needs to be bonded if it might become energized.

It should not take long to do and should not cost much. So there is little reason to not do it.

Top
#91869 - 02/12/05 07:57 AM Re: Structural Steel
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Okay George, with a name like that, I know you know what your talking about At what point is it likely to be energized? Does the steel beam in a basement of a home need to be bonded??

[This message has been edited by George Little (edited 02-12-2005).]
_________________________
George Little

Top
#91870 - 02/12/05 12:38 PM Re: Structural Steel
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
 Quote:
250.102(C) Structural Steel. Exposed structural steel that is interconnected to form a steel building frame and is not intentionally grounded and may become energized shall be bonded ...

A single column supporting a beam is not a steel building frame and the code does not require bonding.
Don
_________________________
Don(resqcapt19)

Top
#91871 - 02/12/05 01:23 PM Re: Structural Steel
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Don- I agree with you but we have inspectors out there that are asking that this steel be bonded and I just wonder where they are coming from???
_________________________
George Little

Top
#91872 - 02/12/05 05:26 PM Re: Structural Steel
George Offline
Member

Registered: 02/23/02
Posts: 380
George Little ---

"may become energized" is the rub. If you lay cables or conduit over or along the steel beam, I would lean toward "may". If no cables or conduit run over or along the beam, I would lean toward "may" not.

I don't see enough support in the code to support your position in an appeal.

Top
#91873 - 02/12/05 09:38 PM Re: Structural Steel
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
George,
Just the fact that isolated steel may become energized does not trigger the requirement for bonding. The bonding requires both the possibility that the steel may become energized and that the steel be an interconnected building frame
Don
_________________________
Don(resqcapt19)

Top
#91874 - 02/13/05 06:59 AM Re: Structural Steel
George Offline
Member

Registered: 02/23/02
Posts: 380
resqcapt19 ---

I believe that wall switches are bonded because the tiny metal screw in the plastic plate might become energized, provides reasonable support for my position.

If I were inspecting and found this isue, I would point out the need and let the contractor do what he will.

Top
#91875 - 02/13/05 08:35 AM Re: Structural Steel
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
George you are worrying me now, are you the type of inspector that makes the rules up as you go along?

Don already went over this I will try to make it clearer.

2002 NEC
 Quote:
250.104(C) Structural Steel. Exposed structural steel that is interconnected to form a steel building frame and is not intentionally grounded and may become energized shall be bonded to the service equipment enclosure, the grounded conductor at the service, the grounding electrode conductor where of sufficient size, or the one or more grounding electrodes used. The bonding jumper(s) shall be sized in accordance with Table 250.66 and installed in accordance with 250.64(A), (B), and (E). The points of attachment of the bonding jumper(s) shall be accessible.


In order for you to be able to require any electrician to bond steel it has to meet all of the following.

It must be exposed

AND

It has to form the steel frame of the structure.

AND

It has to be likely to be energized.

The opening post asked this;

 Quote:
Does a steel I Beam supported by steel post setting on concrete need to be bonded?


If that is the extent of the steel you have no authority to ask for it to be bonded.

I do not take the term "may become energized" to be all encompassing.

In my opinion you would have to show a way or reason it may become energized.

 Quote:
"may become energized" is the rub. If you lay cables or conduit over or along the steel beam, I would lean toward "may".


You do require conduit to be grounded and you do require proper supports for cable systems right?

So how would this lonely piece of steel become energized?

Bob





[This message has been edited by iwire (edited 02-13-2005).]
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#91876 - 02/13/05 09:52 AM Re: Structural Steel
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
I tend to side with Bob on this one. "May become enrgized" could open up a can of worms similar to what we do at a swimming pool. We could be bonding handrails, doors and shelving if we are looking at everyone who is not careful with their Christmas lights and cell phone chargers. If there is electrical utilization equipment hanging on that beam I would want to see the EGC bonded to the beam (the EGC of the circuit likely to energize... yada yada) but if this is a properly supported and routed wiring method simply passing near the beam, I don't see the problem.