#91852 - 02/09/05 08:20 AM 4160 volt conductor rateings
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 822
Loc: Michigan
Table 310.73 2001-5000 volts M.V.105.
500kcmil =530 amps for derateing 475 for terms(110.40). As i see it no derateing for a bank of pipes in open air. Thus 2000 amp requirement = 4 sets 530x4=2120
or 4 sets 475= 1900 amps.
240.101 states fuse can be 3 times conductors ampacity breaker or electronically actuated fuse up to 6 times.


So as I see it conductors must be rated for the ampacity of the true load. Over current protection can be higher then conductor rateings.
The highter amps rateing 105% for derateing only the 90% rateing for terms.
so if load is 1900 amps or below 500s can be used ,fused at 2000 amps.
Top
2017 / 2014 NEC & Related Books and Study Guides
#91853 - 02/10/05 10:28 AM Re: 4160 volt conductor rateings
Bob Offline
Member
Registered: 02/05/02
Posts: 182
Loc: Mobile, AL, USA
Yoopersup
What is the load your are working with?
Top
#91854 - 02/11/05 04:58 AM Re: 4160 volt conductor rateings
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 822
Loc: Michigan
Last sentence says 1900 amps or below.
Top

Member Spotlight
Member Since: 01/22/05
Posts: 5316
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 121 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals