The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Forum Software Upgrade coming soon...
by Webmaster
Today at 12:03 AM
Re: Fabricating Guards out of Lexan?
by frank
Yesterday at 04:11 PM
Would ELV branch circuits be a good idea?
by gfretwell
Yesterday at 01:26 PM
Why cables look like they do
by Texas_Ranger
Yesterday at 12:33 PM
100% breakers?
by Texas_Ranger
01/16/17 06:13 AM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
HotLine1 20
Webmaster 20
gfretwell 13
Trumpy 12
ghost307 12
Who's Online
0 registered (), 0 Guests and 36 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#91852 - 02/09/05 08:20 AM 4160 volt conductor rateings
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
Table 310.73 2001-5000 volts M.V.105.
500kcmil =530 amps for derateing 475 for terms(110.40). As i see it no derateing for a bank of pipes in open air. Thus 2000 amp requirement = 4 sets 530x4=2120
or 4 sets 475= 1900 amps.
240.101 states fuse can be 3 times conductors ampacity breaker or electronically actuated fuse up to 6 times.


So as I see it conductors must be rated for the ampacity of the true load. Over current protection can be higher then conductor rateings.
The highter amps rateing 105% for derateing only the 90% rateing for terms.
so if load is 1900 amps or below 500s can be used ,fused at 2000 amps.

Top
2017 / 2014 NEC & Related Books and Study Guides
#91853 - 02/10/05 10:28 AM Re: 4160 volt conductor rateings
Bob Offline
Member

Registered: 02/05/02
Posts: 182
Loc: Mobile, AL, USA
Yoopersup
What is the load your are working with?

Top
#91854 - 02/11/05 04:58 AM Re: 4160 volt conductor rateings
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
Last sentence says 1900 amps or below.

Top