#91799 - 02/06/05 08:28 AM Article 760 Fire Alarm Systems and NFPA 72
Joe Tedesco Offline
Member
Registered: 10/07/00
Posts: 2749
Loc: Boston, Massachusetts USA
How does the NFPA Fire Alarm Code 72 interface with the NEC?

Does the FA alarm installer have to comply with the NEC, other that Article 760?

I will appreciate some feed back please.

I see and have always approached these systems as emergency systems, and find many areas that are often overlooked.

In Massachusetts we have a C and D license classification for these installers, contractor and journeyman.

Here's a site that includes a test for the FA installer:
http://www.ieisa.com/
_________________________
Joe Tedesco, NEC Consultant
Top
2017 / 2014 NEC & Related Books and Study Guides
#91800 - 02/06/05 06:13 PM Re: Article 760 Fire Alarm Systems and NFPA 72
Ron Offline
Member
Registered: 03/13/02
Posts: 582
Loc: White Plains, NY
Unfortunately the information relationship is a bit muddy between NFPA 70 and 72. Usually some building or life safety code tells you where detection is required and other aspects of the big picture, then 72 gives more application information of where and how to's, then 70 tells you about cable/wire, raceway, boxes, etc. The information in 70 is not only in 760 but in the multiple references to articles in Chapters 1-4. There is even a new smoke detector related requirement that shows up beginning in 2002, that is hiding in 645, if you frequent that part of the code.
_________________________
Ron
Top
#91801 - 02/06/05 07:00 PM Re: Article 760 Fire Alarm Systems and NFPA 72
Joe Tedesco Offline
Member
Registered: 10/07/00
Posts: 2749
Loc: Boston, Massachusetts USA
Thanks for the information Ron:

Quote:
Ventilation in the underfloor area is used for the information equipment room only. The ventilation system shall be so arranged, with approved smoke detection devices, that upon the detection of fire or products of combustion in the underfloor space the circulation of air will cease.

Commentary: This requirement has been revised for the 2002 Code. The underfloor area is required to be provided with smoke detection device(s). Upon detection of smoke, the circulation of air in the underfloor area must be interrupted. The most common method of interrupting air circulation is to open the circuit that supplies power to the air circulation fan.

In addition to causing cessation of air circulation in the underfloor area, the smoke detectors may provide other fire protection functions as part of a complete building fire alarm system.
_________________________
Joe Tedesco, NEC Consultant
Top
#91802 - 02/06/05 08:12 PM Re: Article 760 Fire Alarm Systems and NFPA 72
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
I find it interesting that the smoke detector only has to interrupt the air flow. It isn't required to initiate any audible or visual signals. Kinda drives home ther difference between a smoke detector and a smoke alarm.
_________________________
George Little
Top
#91803 - 02/08/05 12:10 PM Re: Article 760 Fire Alarm Systems and NFPA 72
Ron Offline
Member
Registered: 03/13/02
Posts: 582
Loc: White Plains, NY
If a FACP is required by the building code, then detectors installed in the building need to be connected to it and sound the notification devices. See IBC-2003 907
_________________________
Ron
Top
#91804 - 02/08/05 01:28 PM Re: Article 760 Fire Alarm Systems and NFPA 72
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
Is it possible tp install smoke detectors without installing a FACP? In other words, can I use a smoke detector to control a relay and thus break a set of contacts and drop out the fan and stop the air circulation in the "Computer room"?
_________________________
George Little
Top
#91805 - 02/08/05 01:38 PM Re: Article 760 Fire Alarm Systems and NFPA 72
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
Quote:
How does the NFPA Fire Alarm Code 72 interface with the NEC?
Does the FA alarm installer have to comply with the NEC, other that Article 760?

I will appreciate some feed back please.


Joe I install a fair amount of fire alarm systems and have not looked at NFPA 72 more than a couple of times.

The reason is this, I install the systems per engineered prints.

Even when we do a design build job the fire alarm prints are drawn up by an engineer. After that they go to the FD for approval.

Out at the job I get a stamped set of drawings that I can not deviate from.

The placement of devices, the number of them, how they interact with other building systems like HVAC, elevators etc. is all laid out for me.

All the issues I have input in are contained in the NEC.

Sadly that makes me just an installer and not a technician in my mind.

To be honest I do not feel qualified to design a life safety system like a fire alarm.

Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#91806 - 02/08/05 02:51 PM Re: Article 760 Fire Alarm Systems and NFPA 72
Joe Tedesco Offline
Member
Registered: 10/07/00
Posts: 2749
Loc: Boston, Massachusetts USA
Thanks for the feedback, I was involved in a Basic Fire Alarm Class and most of the students were electricians, some journeymen one master and a few apprentices. They too did not use NFPA 72, and when I mentioned the NEC Article 760, 300.21, 22, and 23 and other rules as they're aware, their face's all dropped.

Am I missing something, or is our trade going downhill?
_________________________
Joe Tedesco, NEC Consultant
Top
#91807 - 02/08/05 03:28 PM Re: Article 760 Fire Alarm Systems and NFPA 72
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
I don't know if I would characterize it as going down hill, although they should be following the NEC sections you quoted.

In my mind the design of modern fire alarm systems is so complex at this point that it needs to be handled by specialists in that field.

The risk are to great and the issues can be complex.

Once you get into larger buildings with smoke evac, elevators, building automation systems, rooms in buildings with separate pre action systems, the list is endless you need someone who really knows their stuff.

The energy codes are forcing the lighting systems to shut down all the lighting when not in use so now we need a tie from the fire alarm to the lighting controls.

Elevators, you have primary and alternate floor recalls which has to be properly programed into the panel.

When we have banks of elevators the emergency generator may only be sized to run one at a time now recall must be coordinated with the specialized elevator power transfer switch.

I am happy to work of a detailed set of prints, I still have to know and follow the NEC and it still takes a craftsman to make it look good and operate correctly.


Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#91808 - 02/08/05 05:39 PM Re: Article 760 Fire Alarm Systems and NFPA 72
Ron Offline
Member
Registered: 03/13/02
Posts: 582
Loc: White Plains, NY
From a business perspective, an electrician should have a copy of NFPA 72, and be somewhat familiar with it in order to get extras! For some reason there might be 900 smoke detector on the project, and if I missed one on the Contract Drawing, that is picked up by the EC, the one extra detector always costs $2,000! I'm being funny , but there is lots on $$$ in change orders if you can pickup on missing stuff.
Of course I'm glad that not to many folks know 72, so that when I screw up on a design, it doesn't get thrown in my face.
That concept applies to many areas of NFPA 70 too!
_________________________
Ron
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 90 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Stack, Scotto, Freecrowder, clee512, Jdscott2005

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals