The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
International Wire Colour Codes
by Texas_Ranger
Today at 08:24 AM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
230 or 345 kV transmission lines?
by annemarie1
10/12/16 01:23 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
HotLine1 6
renosteinke 6
ghost307 5
Potseal 4
Who's Online
1 registered (hyetal), 201 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#91780 - 02/03/05 02:02 PM 3-way exhaust fan disconnect
Elzappr Offline

Registered: 12/20/01
Posts: 273
Loc: Oregon
Can a 3-way switch set serve as a disconnect for a small exhaust fan?
Since the code allows (225.38 exception) 3-ways for a residential garage disconnect, it would seem ok to do the same for the exhaust fan. Yet, it seems a bit dangerous to rely of turning off the circuit with a 3-way, and hoping that someone doesn't come along and flip the out-of-sight switch while you are working on the wiring.

2014 / 2011 NEC & Related Books and Study Guides
#91781 - 02/03/05 02:17 PM Re: 3-way exhaust fan disconnect
iwire Offline

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
No a 3 way switch can not be a disconnecting means.

A disconnecting means must have a clearly labeled off or open position.

Depending on your exhaust fan one of these will apply.

422.35 Switch and Circuit Breaker to Be Indicating.
Switches and circuit breakers used as disconnecting means shall be of the indicating type.

430.104 To Be Indicating.
The disconnecting means shall plainly indicate whether it is in the open (off) or closed (on) position.
Bob Badger
Construction & Maintenance Electrician

#91782 - 02/03/05 02:31 PM Re: 3-way exhaust fan disconnect
Tom Offline

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
If you approach this strictly as a motor load, 430-104 requires the disconnecting means to "plainly indicate whether it is in the open(off)..." 430-109 Exception 2 would be the required disconnect (branch circuit breaker), since most of these exhaust fans have very small motors.

Or, if the fan is an appliance, which, IMO it is, then 422.31(A) applies iand you still end up with the branch breaker being the disconnect.

(and while I'm looking this up, IWire beats me to the punch)

[This message has been edited by Tom (edited 02-03-2005).]
Few things are harder to put up with than the annoyance of a good example.

#91783 - 02/03/05 03:11 PM Re: 3-way exhaust fan disconnect
Elzappr Offline

Registered: 12/20/01
Posts: 273
Loc: Oregon
Ok, so if the motor is dinky (<1/8hp) and the branch circuit breaker serves as the REQUIRED disconnect, are the 3-ways illegal? Are the 3-ways considered just a controller, since they aren't adequate as a positive means for isolating the motor?


ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals