The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Correct rotation, wrong sequence
by Potseal
Yesterday at 03:14 PM
Industrail Control Panel bonding per 409.108
by sparkyinak
12/09/16 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
New in the Gallery:
12.5A through 0.75mm flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
HotLine1 10
Potseal 9
sparkyinak 8
Texas_Ranger 7
Who's Online
0 registered (), 224 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#91749 - 02/03/05 07:52 AM Dryer receptacles - was this ever allowed?
BPiersel Offline
Member

Registered: 01/06/05
Posts: 18
Loc: Minnesota
Hello,

I recently bought an older house, and I have been finding problems with the wiring in the breezeway and garage that was added on in the 80’s. It appears to have been a lot of DIY work that never got inspected properly. The most recent one I have found is with the dryer receptacle. This is a 10-30R (3-wire) receptacle fed from a subpanel. I know that this is not allowed by 2002 NEC, but was the 3-wire receptacle ever allowed when fed from a subpanel? I thought it was only allowed when fed from the main panel, since neutral and ground are bonded together there. I’m just wondering if this may have been allowed by code when it was installed or if it is another example of incorrect wiring. I plan to replace it with a 14-30R, since the cable has 3 conductors plus the ground.

Brian

Top
2014 / 2011 NEC & Related Books and Study Guides
#91750 - 02/03/05 10:01 AM Re: Dryer receptacles - was this ever allowed?
dana1028 Offline
Member

Registered: 01/09/02
Posts: 163
Loc: San Carlos, CA
"but was the 3-wire receptacle ever allowed when fed from a subpanel? I thought it was only allowed when fed from the main panel"

3-wire receptacles (i.e. using the neutral to ground dryer frames) was permitted up until 1996 (?); they were permitted to originate in any panel as long as the neutral was insulated.

Quite freguently SE cable was used to wire up stoves, ovens, dryers. Some of this cable did not have an insulated grounded (neutral) conductor. You were not permitted to use this type cable inside a house unless: you were feeding stoves, ovens, dryers and the circuit originated in the service.

See 1979 - 250-60(C) & 338-3(b)

Top
#91751 - 02/03/05 02:33 PM Re: Dryer receptacles - was this ever allowed?
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
I was always told 3 wire range and dryer feeds where not permitted from sub panels, I will have to check my local amendments.

[This message has been edited by iwire (edited 02-03-2005).]
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#91752 - 02/03/05 02:54 PM Re: Dryer receptacles - was this ever allowed?
mike d Offline
Junior Member

Registered: 01/04/05
Posts: 9
Loc: new jersey
this was common, look at 250.140 (3) in the 2002 NEC applies to existing ranges & dryers, if the grounded conductor is uninsulated it must originate at the service
equipment, and also look at 250.42 (B) exception #1 permits load side grounding, on existing ranges & dryers,

Top
#91753 - 02/06/05 06:39 AM Re: Dryer receptacles - was this ever allowed?
CharlieE Offline
Member

Registered: 04/23/04
Posts: 204
Loc: Indianapolis
It was permitted to feed them from a distribution panelboard but it was not permitted to use SE cable from that location. You were required to use a cable with an insulated neutral.

- - - - - - - - - - - - - - - - - - - - - - - - - - -
Charlie Eldridge, Indianapolis, Utility Power Guy
_________________________
Charlie Eldridge, Indianapolis Utility Power Guy

Top
#91754 - 02/06/05 06:48 AM Re: Dryer receptacles - was this ever allowed?
cpal Offline
Member

Registered: 05/17/04
Posts: 165
Loc: Cohasset MA
My 1996 NEC in Article 250.60(c) States
The grounded conductor is insulated and part of Type SE service-entrance cable and the branch circuit originates at the service equipment.

This language was removed in the 99

Charlie

Top
#91755 - 02/07/05 08:15 AM Re: Dryer receptacles - was this ever allowed?
BPiersel Offline
Member

Registered: 01/06/05
Posts: 18
Loc: Minnesota
Thanks for the info, everyone.

If the neutral has to be insulated from a subpanel, wouldn't there always be a separate grounding conductor in the cable, so you'd always end up running a total of 4 conductors from the subpanel? Since you'd always have the separate neutral and ground conductors, the only real reason to put a 3-wire receptacle fed from a subpanel would be to avoid changing the appliance cord, which I assume was the reason in this case.

Brian

Top
#91756 - 02/07/05 09:26 AM Re: Dryer receptacles - was this ever allowed?
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
Long ago I asked why you would run 10-3/wg to a 3 prong dryer outlet and the answer was that since the 3d wire is identified as a groundED conductor it had to be white, even tho it was also used as a groundING conductor. They usually attached the bare wire to the backstrap of the receptacle and the white to the ground contact. Once "the war was over" it is easy to go to the 4 pronger.
_________________________
Greg Fretwell

Top